TAC Xenta Device Plug-In: Could not generate MTA application.
  • TAC Xenta Device Plug-In: Could not generate MTA application.
‎2018-09-09 10:07 PM
In the TAC Vista System Plug-In, a programmable controller is configured through the Xenta Device Plug-In. Browsing to a Menta file on the hard drive should associate that application with the controller to be uploaded to the database later. Instead, an error message is displayed:
  • TAC Vista System Plug-In
  • Xenta programmable controller
  • Xenta 280, 281, 282, 283, 300, 301, 302, 401, 401:B
  • Menta
An error in the Menta file is keeping it from generating the necessary background files for the download to occur.
  1. Open the Menta file
  2. Go to Options > Simulate
  3. If no error occurs, choose Commands > Generate
  4. Either at simulation or at generation, an error should be highlighted in the Menta file that is responsible for the failure to generate.
  5. Fix this error and save the Menta file back to the hard drive.
  6. Attempt to browse in the Menta file again.
  • 5274