TAC Vista trend chart settings aren't saved
  • TAC Vista trend chart settings aren't saved
  • sesa177673
    sesa177673
  • sesa150561
    sesa150561
‎2018-09-06 03:28 PM
Trend chart settings aren't saved. The properties dialogue is opened by right-clicking on the open trend chart and then one or more of the settings are changed. After that OK is pressed and then the chart is saved using the save button.
TAC Vista
TAC Vista 5.1.7.
It appears that the new settings aren't being saved, but by clicking the save button before refreshing the trend chart the current "view" is saved - not the new settings entered in the properties dialogue.
  1. Change the settings as described
  2. Click OK when finished with the settings
  3. Refresh the trend chart immediately
  4. Save it. The view with the new settings will be saved.
Another option in Windows 7:
  1. Right click on the chart object.
  2. Go to the "general" tab
  3. Uncheck Autoscale
  4. Enter the desired value.
  • 7663