TAC Vista
When you used LNS in older version of TAC Vista there was a checkbox in in the network object that had to be unchecked so that TAC Vista would not overwrite address table information and address information when downloading application.
This setting is still there and if you have a upgraded system sometimes this is left unchecked.
  1. Hold down ctrl-shift and select properties on the network object.
  2. Check the checkbox "ADDRMGMT"