System Limitations of Flex Server
  • System Limitations of Flex Server
  • pranavkumar003
    pranavkumar003
  • CraigEl
    CraigEl
pranavkumar003 Cadet
‎2025-05-15 12:23 AM
Last Updated: Administrator CraigEl Administrator ‎2025-05-15 12:30 AM
This document gives guidelines on the device constraints that effect the system capabilities or the system limitations of the Flex Server.
EcoStruxure Building Activate
  • EcoStruxure Building Activate Flex Server
  • EcoStruxure Building Activate Partner Portal
Understanding this document helps in efficiently designing architecture and Single line Diagrams.
Identifying potential bottlenecks in a system allows for preemptive action. If you know a system parameter has limited device capacity, you can optimize the distribution methods or plan for upgrades before it becomes a critical issue. Understanding the limitations of system allows for the implementation of backup measures.
Thes guidelines provide the recommended Flex Server design limits for common applications. These are the configurations that have been tested and supported by Schneider Electric. Environmental factors such as network traffic and radio interference may reduce the stated limits of these guidelines. Deviations from these guidelines may result in performance related issues or product failures.
Flex Server Capacity
Parameter Maximum Number
Number of total devices (all protocols combined) 50
Number of controlled points (all protocols combined) 500
BACnet
Number of BACnet MSTP devices per RS485 port 32a b e
Number of BACnet MSTP networks per server 2c
Number of BACnet IP devices 50d e
a. Maximum number of devices according to protocol specifications and guidelines.
b. BACnet MS/TP adheres to RS485 rules for wiring, wire type, termination etc.
c. There is one onboard RS485 port, an additional port can be added via USB.
d. BACnet IP uses default UDP port 47808 (0xBAC0).
e. The total number of devices across all protocols must not exceed 50
Modbus
Number of Modbus RTU devices per RS485 port 32a b e
Number of Modbus RTU networks per server 2c
Number of Modbus TCP devices 50d e
b. Modbus RTU adheres to RS485 rules for wiring, wire type, termination etc.
d. Modbus TCP uses default TCP port 502.
LoRaa
Number of LoRa sensors per server 32b c d
Maximum number of messages per day (per server) 100
a. LoRa distances – LoRa is noted for its long range and deep penetration. LoRa transmissions can penetrate glass, metal and concrete found in most buildings. The radio’s antenna and installation can affect the range of LoRa sensors. You must test the transmission and signal strength, when installing wireless devices.
b. Maximum number of devices according to protocol specifications and guidelines.
c. Every LoRaWAN sensor manufacturer has their own decoder.
d. The total number of devices across all protocols must not exceed 50
SNMP
Number of SNMP devices 10a
Maximum number of messages per day (per server) 1024
a. The total number of devices across all protocols must not exceed 50
Object Limits
Object Type Maximum Number
Analog values 500a
Digital values 500a
Multi-state values 500a
Analog Input 500a
Multi-state input 500a
Analog output 500a
Digital output 500a
Multi-state output 500a
a. The total number of combined points must not exceed 500
  • PranavKumar25