Issue
This document gives guidelines on the device constraints that effect the system capabilities or the system limitations of the Flex Server.
Product Line
EcoStruxure Building Activate
Environment
- EcoStruxure Building Activate Flex Server
- EcoStruxure Building Activate Partner Portal
Cause
Understanding this document helps in efficiently designing architecture and Single line Diagrams.
Identifying potential bottlenecks in a system allows for preemptive action. If you know a system parameter has limited device capacity, you can optimize the distribution methods or plan for upgrades before it becomes a critical issue. Understanding the limitations of system allows for the implementation of backup measures.
Resolution
Thes guidelines provide the recommended Flex Server design limits for common applications. These are the configurations that have been tested and supported by Schneider Electric. Environmental factors such as network traffic and radio interference may reduce the stated limits of these guidelines. Deviations from these guidelines may result in performance related issues or product failures.
Flex Server Capacity
Parameter | Maximum Number |
Number of total devices (all protocols combined) | 50 |
Number of controlled points (all protocols combined) | 500 |
BACnet
Parameter | Maximum Number |
Number of BACnet MSTP devices per RS485 port | 32a b e |
Number of BACnet MSTP networks per server | 2c |
Number of BACnet IP devices | 50d e |
a. Maximum number of devices according to protocol specifications and guidelines.
b. BACnet MS/TP adheres to RS485 rules for wiring, wire type, termination etc.
c. There is one onboard RS485 port, an additional port can be added via USB.
d. BACnet IP uses default UDP port 47808 (0xBAC0).
e. The total number of devices across all protocols must not exceed 50
Modbus
Parameter | Maximum Number |
Number of Modbus RTU devices per RS485 port | 32a b e |
Number of Modbus RTU networks per server | 2c |
Number of Modbus TCP devices | 50d e |
a. Maximum number of devices according to protocol specifications and guidelines.
b. Modbus RTU adheres to RS485 rules for wiring, wire type, termination etc.
c. There is one onboard RS485 port, an additional port can be added via USB.
d. Modbus TCP uses default TCP port 502.
e. The total number of devices across all protocols must not exceed 50
LoRaa
Parameter | Maximum Number |
Number of LoRa sensors per server | 32b c d |
Maximum number of messages per day (per server) | 100 |
a. LoRa distances – LoRa is noted for its long range and deep penetration. LoRa transmissions can penetrate glass, metal and concrete found in most buildings. The radio’s antenna and installation can affect the range of LoRa sensors. You must test the transmission and signal strength, when installing wireless devices.
b. Maximum number of devices according to protocol specifications and guidelines.
c. Every LoRaWAN sensor manufacturer has their own decoder.
d. The total number of devices across all protocols must not exceed 50
SNMP
Parameter | Maximum Number |
Number of SNMP devices | 10a |
Maximum number of messages per day (per server) | 1024 |
a. The total number of devices across all protocols must not exceed 50
Object Limits
Object Type | Maximum Number |
Analog values | 500a |
Digital values | 500a |
Multi-state values | 500a |
Analog Input | 500a |
Multi-state input | 500a |
Analog output | 500a |
Digital output | 500a |
Multi-state output | 500a |
a. The total number of combined points must not exceed 500