System Limitations of Flex Server

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • System Limitations of Flex Server
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • pranavkumar003
    pranavkumar003
  • CraigEl
    CraigEl

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
126 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

System Limitations of Flex Server

Shuttle Bay pranavkumar003 Shuttle Bay
‎2025-05-15 12:23 AM

Last Updated: Administrator CraigEl Administrator ‎2025-05-15 12:30 AM

 

Issue

This document gives guidelines on the device constraints that effect the system capabilities or the system limitations of the Flex Server. 

Product Line

EcoStruxure Building Activate

Environment

  • EcoStruxure Building Activate Flex Server
  • EcoStruxure Building Activate Partner Portal

Cause

Understanding this document helps in efficiently designing architecture and Single line Diagrams.

Identifying potential bottlenecks in a system allows for preemptive action. If you know a system parameter has limited device capacity, you can optimize the distribution methods or plan for upgrades before it becomes a critical issue. Understanding the limitations of system allows for the implementation of backup measures.

Resolution

Thes guidelines provide the recommended Flex Server design limits for common applications. These are the configurations that have been tested and supported by Schneider Electric. Environmental factors such as network traffic and radio interference may reduce the stated limits of these guidelines. Deviations from these guidelines may result in performance related issues or product failures.

 

Flex Server Capacity

Parameter Maximum Number
Number of total devices (all protocols combined) 50
Number of controlled points (all protocols combined) 500

 

BACnet

Parameter Maximum Number
Number of BACnet MSTP devices per RS485 port 32a b e
Number of BACnet MSTP networks per server 2c
Number of BACnet IP devices 50d e

 

a. Maximum number of devices according to protocol specifications and guidelines.

b. BACnet MS/TP adheres to RS485 rules for wiring, wire type, termination etc.

c. There is one onboard RS485 port, an additional port can be added via USB.

d. BACnet IP uses default UDP port 47808 (0xBAC0).

e. The total number of devices across all protocols must not exceed 50

 

Modbus

Parameter Maximum Number
Number of Modbus RTU devices per RS485 port 32a b e
Number of Modbus RTU networks per server 2c
Number of Modbus TCP devices 50d e

 

a. Maximum number of devices according to protocol specifications and guidelines.

b. Modbus RTU adheres to RS485 rules for wiring, wire type, termination etc.

c. There is one onboard RS485 port, an additional port can be added via USB.

d. Modbus TCP uses default TCP port 502.

e. The total number of devices across all protocols must not exceed 50

 

LoRaa

Parameter Maximum Number
Number of LoRa sensors per server 32b c d
Maximum number of messages per day (per server) 100

 

a. LoRa distances – LoRa is noted for its long range and deep penetration. LoRa transmissions can penetrate glass, metal and concrete found in most buildings. The radio’s antenna and installation can affect the range of LoRa sensors. You must test the transmission and signal strength, when installing wireless devices.

b. Maximum number of devices according to protocol specifications and guidelines.

c. Every LoRaWAN sensor manufacturer has their own decoder.

d. The total number of devices across all protocols must not exceed 50

 

SNMP

Parameter Maximum Number
Number of SNMP devices 10a
Maximum number of messages per day (per server) 1024

 

a. The total number of devices across all protocols must not exceed 50

 

Object Limits

Object Type Maximum Number
Analog values 500a
Digital values 500a
Multi-state values 500a
Analog Input 500a
Multi-state input 500a
Analog output 500a
Digital output 500a
Multi-state output 500a

 

a. The total number of combined points must not exceed 500

Labels (1)
Labels:
  • EcoStruxure Building Activate
Tags (1)
  • Find more articles tagged with:
  • PranavKumar25
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of