System License Information shows zero (0) Activated Count

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • System License Information shows zero (0) Activated Count
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2434 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

System License Information shows zero (0) Activated Count

Picard RobertAndriolo Picard
‎2024-03-27 07:13 PM

Last Updated: Crewman ContentModerator ‎2025-09-01 03:32 AM

Issue

When viewing License Information, the Activated count still shows 0 for all features.

Product Line

EcoStruxure Building Operation

Environment

  • Building Operation License Administrator
  • Building Operation License Server

Warning

Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support for assistance.

Cause

There are multiple causes for this, as we are aware:

  • Running Demo license
  • License Server not running / uninstalled.  It is possible to activate licenses and then uninstall the License Server, and licenses will still be active and available to EBO components.  
  • Firewall setting

Recently, we have located an issue where multiple paths exist for the License Server in the Windows Registry. The specifics of how this occurs is still unknown, but it has been seen on a few installations.  

Resolution

Before starting, remove the demo license and restart the license server.  The systems, that is, the Enterprise Central/Server, will continue to run until the servers are restarted.   This will be necessary after completing the registry reset. 

 

SBO License Server Reset Has been updated to check the known locations of the registry and provide the ability to make these entries the same as those entered in the License Administrator

RobertAndriolo_0-1711591363679.png

 

 

 A pop-up will appear during the initial running of the Reset Tool to indicate this, as shown below.

RobertAndriolo_1-1711591528626.png

 

If the tool is unavailable or you wish to check this manually, then a Windows Registry search for the key TACLIC_LICENSE_FILE and its data should show its value and indicate the different (or the same) paths.

TACLIC_LICENSE_FILE.png

Updating the TACLIC_LICENSE_FILE data to match the License Server path shown in the License Administrator should resolve the issues.  

 

SBO License Setup

This registry check is also included in the SBO License Setup tool.  In this instance, it automatically details the changes.  After selecting OK (in the screenshot below), you'll have the option to Apply (or cancel) any of the changes applied by the tool.

 
RobertAndriolo_0-1712017099258.png
 

 

 

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (1)
  • Find more articles tagged with:
  • RobertAndriolo24
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore