Synchronizing time in Vista Server and a Xenta server when running on a Domain
  • Synchronizing time in Vista Server and a Xenta server when running on a Domain
  • SESA116857
    SESA116857
‎2018-09-06 03:02 PM
  • Xenta Server
  • Xenta 511, 527, 701, 711, 721, 731, 913
  • Vista Server
  • Domain network
If your computer is running on a domain network then the computer cannot be manually configured to use a Xenta server or an external Time Server as its time source.
To get your Xenta Server and Vista Server to use the same time you have the following options:
  1. Take the Vista Server off of the domain and configure the PC to use the Xenta Server as its time server.
  2. Set the Domain controller to use the same SNTP server that the Xenta Server is using. This requires that the network open the ports to communicate with the SNTP server.
  3. Install a hardware SNTP server or run a software SNTP server that gets its' time from the domain controller and set the Xenta server to communicate with this hardware/software SNTP server.
  • 2353