Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Support of Control Description Command delays in SubLAN devices.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Support of Control Description Command delays in SubLAN devices.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1214 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Support of Control Description Command delays in SubLAN devices.

Picard Product_Support
‎2018-09-10 01:19 AM

Last Updated: Crewman ContentModerator ‎2025-09-25 03:05 AM

Issue

Is it possible to use Control Description (command) delays on MR controllers?

MR (Micro Regulator) DO points not turning ON (or not turning OFF) - sticking.

Environment

I/NET Seven

MR (Micro Regulator) Controllers

Cause

The Control Description command delay was not implemented in the MR as it was not intended to be used for control of multiple high power devices, which this feature was designed for; also, the MR does not have the memory capability to support the timer queue to handle it.

Note: The Control Description command delay does function within the SLI (7793 / 7798B1 / 7798C) although this function is supported here it is not intended for the control of multiple subLAN devices, such as the MR.  You should not rely on this control function from the SLI.  Undesired results can be expected if this is implemented and is not supported.

Resolution

The Control Description Command Delay is not supported within subLAN devices and should not be implemented.  Alternative methods of delaying startup of control devices are:

  • Using Time schedules; the Master / Slave time schedules feature.  Within the slave schedules you are able to delay / adjust the start time by minutes. The combination of using Master / Slave ATS and Host ATS provides a powerful and simple user interface in modifying all the Master Schedules from a single location. Refer to TCON 300 Chapters 4 and 7.
  • MR Functions (DDC); If your control delays are required within the MR, a method available to use is the MR-DDC Relay modules are the delay before break (DDB) or delay before make (DBM) timers.  An even simpler method would be to stagger scan rates (using prime numbers) within your MR Function DDC modules.  Refer to TCON 300 Chapter 13. The DDC modules have there own scan rates and control the point based on this scan rate and will override any Resident I/O Point scan rate defined on these output points.
  • Programmer timers from within the SLI which the control critical items of plant and require a staggered startup procedure.
Labels (1)
Labels:
  • TAC INET
Tags (1)
  • Find more articles tagged with:
  • 5797
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore