Suggested configuration for Xenta 121, STR-150 in single occupancy zones (Hotel Operation)

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Suggested configuration for Xenta 121, STR-150 in single occupancy zones (Hotel Operation)
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2347 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Suggested configuration for Xenta 121, STR-150 in single occupancy zones (Hotel Operation)

Picard Product_Support
‎2018-09-10 12:08 AM

Issue

Suggested configuration for Xenta 121, STR-150 in single occupancy zones (Hotel Operation):

  • Single setpoint display for ease of use for hotel guests
  • Erasing setpoint offsets between guests automatically on transition from unoccupied to occupied
  • Disable fan overrides

Product Line

TAC Vista

Environment

  • Hotel rooms
  • Xenta 121, ZBuilder
  • STR-150

Cause

A hotel room is a unique application of the Xenta 121 and must be tailored to fit the temporary residents and be as easy to use and understand via an STR-150 as possible to reduce the amount of calls to the on-call maintenance department.

Resolution

The important thing to remember is that the Xenta 121 and STR-150 do not have duplex communication capabilities. Communication is one way from the stat to the controller. There is no capability for the controller to override/control the stat display. Because of this, it will be very important to standardize setpoints between the stat, the controller, and system-wide.

Set Up the STR-150

Refer to the STR-150 User’s Manual for additional information.
Push the fan and bypass buttons simultaneously for 2 seconds to enter P0. In P0, hold down the bypass button and push the fan button three times. The wrench symbol is lit when the STR-150 is in configuration mode.

Parameter Function Value/Range Set Value
P0 Software Version - -
P1 °C or °F temperature display 1=°C, 2=°F 2
P2 Reference temperature (Reftemp) 15-30°C / 60-90°F 72 1
P3 Setpoint or room temp. as default 1=Setpt, 2=Room 1
P4 Timeout 5-90 seconds 10
P5 Fan settings 0= No fan
1= On/Off fan
2= Two-speed fan
3= Three-speed fan
0 2
P6 Room temperature and setpoint display resolution 0.1 or 0.5°C
0.2 or 1.0°F
0.2
P7 Max adjustable setpoint span above or below Reftemp (P2). ±0 - ±5°C
±0 - ±10°F
10
P8 Bypass button and occupancy indication When = 2, no bypass command is sent to the controller 1= Symbol on, off or flashing
2= Symbol always off
2

1 Reference temperature should equal the average of the Xenta 121 occupied heating and cooling setpoints. Assuming 70°F heating and 74°F cooling for this example.
2 There is no way to give only AUTO/ON override control to hotel guests, so fan override capabilities should be disabled.

Wire STR-150 to Xenta 121

STR-150 Xenta 121
Mode 11 Y1 5
Data 12 X1 7
M 13 M 6

Set Up the Xenta 121 - ZBuilder

Connected devices > Room unit

Select STR-150 and Check the box for "Activate STR-150 reset offset function."
Engineering TAC Xenta 120 Manual Chapter 9.1.2 states:
There is a so-called hotel reset function for room unit STR-150. When activated, an 'old' offset value is not taken into account when going from Unoccupied to Occupied until the Offset is changed (probably by a new hotel guest).

Control > Setpoints

  • Center all control setpoints around reference temperature of the STR-150. In this example, the reference temperature is 72°F, so cooling and heating setpoints have been centered around that.
  • Setpoint calculation mode is set to method A which preserves symmetry around a base setpoint, but since these setpoints are already symmetrical, that is not of great importance.
  • Expose normalize setpoint is important for the hotel staff to see the same setpoint as the stat is displaying to the hotel guest.

Operation

  1. STR-150 defaults to reference temperature as setpoint 72°F. Xenta 121 uses default setpoints. In cooling maintaining 74°F. If the stat is set to display setpoint by default, the customer will only see the setpoint and won't be aware of the 2-degree dead band offset.
  2. Hotel guest decides 72°F is too hot and lowers the setpoint on the stat to 70°F. Xenta 121 interprets this as a -2°F offset on setpoints and now maintains 68°F heating/72°F cooling.
  3. Guest checks out and the room is set to unoccupied. Stat continues to display 70°F but the larger unoccupied dead band actually controls to set default of 80°F for cooling.
  4. Next guest checks in and the room is set to occupied. Stat continues to display 70°F but the Xenta 121 has erased the offset from its calculation and maintains 74°F.
  5. Guest feels this is too warm and lowers the stat from 70°F to 69.8°F. A new offset of -2.2°F is sent to the Xenta 121 which now controls the cooling setpoint to 71.8°F. The guest believes they have lowered their setpoint by 0.2°F  but in reality have effectively lowered it 2.2°F. As soon as they make a change to the setpoint, they resume control of the offsets.
Labels (1)
Labels:
  • TAC Vista
Tags (2)
  • Find more articles tagged with:
  • 5438
  • thermostat
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of