Stand Alone Continuum using SQL Server 2005 Express is not purging the ExtendedLog table

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Stand Alone Continuum using SQL Server 2005 Express is not purging the ExtendedLog table
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2853 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Stand Alone Continuum using SQL Server 2005 Express is not purging the ExtendedLog table

Picard Product_Support
‎2018-09-07 07:36 AM

Last Updated: Crewman ContentModerator ‎2025-09-01 03:38 AM

Issue

After installing a new Stand Alone Continuum system or upgrading it to use SQL Server 2005 Express (SQL Express) it is found that the ExtendedLog table is not being purged. (truncate delete purge)

The tables fill up, resulting in a large Continuum database that can cause the system to slow down as it reaches its 4GB limit.

Product Line

Andover Continuum

Environment

  • Continuum Stand Alone v1.82 and above.
  • Continuum Stand Alone system that has been upgraded from v1.81 or below.
  • SQL Server 2005 Express

Warning

Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support Services for assistance.

Cause

Before Continuum v1.81, our Database engine for Continuum was MSDE. It used SQL Server Agent service to run maintenance tasks on the ContinuumDB. SQL Server 2005 Express does not have this SQL Server Agent and the scheduled maintenance tasks are added as Windows scheduled tasks during the creation of a new Continuum Database.

"SQL Agent is a SQL Server service that is used to automatically schedule job execution for SQL Server. It is typically used to schedule the execution of DTS packages or to perform system maintenance tasks like database backups. While MSDE includes the SQL Agent service, SQL Server 2005 Express does not. However, you can use the Windows built-in Task Scheduler to schedule jobs for SQL Server 2005 Express. You can use Task Scheduler in combination with the downloadable DTS runtime to automatically schedule the execution of DTS packages. Likewise, you can use Task Scheduler in combination with the SQL Server 2005 Express command-line SQLCMD tool to regularly execute SQL Server 2005 Express system maintenance jobs like database backups and other database access jobs."
See full article on this at http://technet.microsoft.com/en-us/library/cc966393.aspx

The key here is that the scheduled tasks are added during the creation of a new Continuum Database. When upgrading Continuum you would typically install overtop the existing installation; upgrading your existing Continuum Database, which does not create the Windows scheduled tasks required to schedule events tables and ExtendedLog table to be truncated on a regular basis.

Resolution

Check Purge interval

First thing to do is to confirm that your Extended Log Purge Interval has actually been set properly, by default this is set to 0 which disables automatic purging.

  1. Right-click your Continuum icon and select General Preferences.
  2. On line 10 - Extended Log Purge Interval, set this to the number of days you want to keep in your database. (typically 30 days)
  3. Once this is set, the next time the scheduled task runs it will truncate your table back to the number of days you have selected.

If this was not set properly this may be all that is required. If it still does not purge and tasks have not been created then continue on with the below steps.

Creating Scheduled Truncation Tasks

Create a new Continuum database, at the end of this creation after closing the Database Initialization window, the scheduled tasks are created under Start -> Accessories -> System Tools -> Scheduled tasks.

To create these scheduled tasks and associated scripts you will need to delete the DB, create a new one, and then restore your backed up database overtop. To do this follow the below steps:

  1. Shut down all Continuum Cyberstations.
  2. IMPORTANT: Make sure to perform a full SQL Database backup before attempting to make any changes to the database. (See Move / Backup / Restore a database on a Single User SQL2005 Express system for details on how to backup your database and, if not already installed, where to get Management Studio from)
  3. Use SQL Management Studio Express and logon with the SA account.
  4. Browse to the Databases folder, right-click the ContinuumDB and select Delete. This will delete the ContinuumDB from the server and the associated .Mdf and .Ldf files from the harddrive.
  5. Open up Database Initialization.
  6. Select Stand Alone.
  7. Click on the Create New database radio button (bottom right) which opens up the needed fields.
  8. Confirm the Database name is ContinuumDB.
  9. Ensure the User Login ID is set to Andover97.
  10. Ensure the User Password is set to (not disclosed due to public access).
  11. Ensure the path is correct for the DB File location.
  12. Enter in the SQL Server's SA password.
  13. Enter the Windows username and password that has local administrator privileges. (IMPORTANT: Make sure that your Windows user has a valid username and password; the scheduled tasks will not be created if the Windows user does not have a password)
  14. Click Continue (This creates the two files ContinuumDev.mdf and ContinuumLog.ldf in the DB File Location)
  15. Click Close to close Database Initialization, this is the point at which the scheduled tasks and associated scripts are automatically created.
  16. Using SQL Management Studio, now restore the backed up database.
    • Restore the backup over the top of the ContinuumDB on your new system:
      Right click on ContinuumDB -> Tasks -> Restore -> Database. Select "From device:" and add your Database file, making sure to tick the Restore checkbox to select the source. Next, go to the Options page and select "Overwrite the existing database" and press the "OK" button.
  17. Change the db owner with the below query using the sp_changedbowner stored procedure. Select "New Query" and copy the query text shown below. Run the query.
    use ContinuumDB
    go
    sp_changedbowner 'Andover97'
    go

Now confirm that your Extended Log Purge Interval is set properly, by default this is set to 0 which disables automatic purging.

  1. Right-click your Continuum icon and select General Preferences.
  2. On line 10 - Extended Log Purge Interval, set this to the number of days you want to keep in your database. (typically 30 days)
  3. Once this is set, the next time the scheduled task runs it will truncate your table back to the number of days you have selected.
Labels (1)
Labels:
  • Andover Continuum
Tags (1)
  • Find more articles tagged with:
  • 4757
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore