Square D Altivar 61 with BACnet card. Found drives coming on and offline on BACnet Bus. The literature stated the baud rate could be up to 76.8 k.
  • Square D Altivar 61 with BACnet card. Found drives coming on and offline on BACnet Bus. The literature stated the baud rate c...
  • DavidChild
    DavidChild
  • sesa119747
    sesa119747
‎2018-09-06 02:29 PM
Last Updated: Sisko DavidChild Sisko ‎2021-02-01 01:48 AM
Communication card would not communicate above 19.2k baud rate.
Change the baud rate of the network below 19.2k.