Specification for using a USRobotics modem with dial application

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Specification for using a USRobotics modem with dial application
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1752 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Specification for using a USRobotics modem with dial application

Picard Product_Support
‎2018-09-06 09:34 PM

Last Updated: Crewman ContentModerator ‎2025-09-25 03:04 AM

Issue

Specification for using a USRobotics modem with dial application

Environment

I/NET site

Cause

What are the specification for using a USRobotics modem with dial application?

Resolution

Warning! Using a non-analog line will damage the modem!

INET Dial Applications using US Robotics (External Modems)

See TCON 101, TCON 213 , TCON 226 and TCON 298 for more details

  1. If the modem has dip switches, set them as follows:
    • 1,5,6, and 7 up
    • 2,3,4, and 8 down
    • If the modem does not have dip switches, don’t worry about it!
  2. PC, modem, and phone line must be connected and "ON"
    • Connect the modem to an analog phone line only.
    • Warning! Using a non-analog line will damage the modem! (Contact USR)
      http://www.usr.com/products/analog/p-56k-menu.asp
  3. Make sure the correct modem driver is installed. Don’t use “Standard Modem”.
  4. Set the hyper-terminal session “Baud” as specified in the following instructions (See the sections titled: “Remote Site Settings” and “Host Settings”)
  5. View the modem’s Active and Stored settings:
    • "ATI4" followed by the Enter key displays the settings the modem is using
    • "ATI5" followed by the Enter key displays the settings stored in NOVRAM
    • If the settings need to be changed then continue
    • Recommend "AT&F" to reset the modem to factory defaults.
    • See the sections titled: “Remote Site Settings” and “Host Settings”
  6. Suggest you store the settings in both profiles of the modem’s NOVRAM.
    • "&W0" stores to "&Y0"
    • "&W1" stores to "&Y1"
  7. Help Commands for US Robotics are:
    • AT&$
    • ATS$
    • AT$
  8. After following the preceding steps for the remote site’s modem:
    1. Connect the modem to the Tap (or emulated Tap) and Analog Phone Line
    2. Power-up the modem
    3. Press the controller’s reset button or cycle the Tap’s power
    4. Do NOT cycle the modem’s power
    5. The "RD" and "SD" should flash after several seconds have past
    6. After about 30 seconds the "AA," TR" and "CS" lights should be "On"
  9. Using INET, Dial the site. Make sure the host can:
    • Dial out (you can hear the dial tone)
    • Handshake with the remote Modem
    • Maintain its connection to the remote modem (Neither modem automatically terminates call)
    • See the Controller(s) on the LAN • Actually connect to the controller(s)
    • View points in the summary screens

 

Remote Site Settings:

DIAL=TONE B0 E0 F1 M1 Q0 V1 X0 Y0
BAUD=9600 PARITY=N WORDLEN=8 

&A0 &B1 &C1 &D2 &G0 &H0 &I0 &K0
&M0 &N6 &P0 &R2 &S0 &T5 &U6 &Y1 

S00=001 S01=000 S02=043 S03=013 S04=010 S05=008 S06=002
S07=060 S08=002 S09=006 S10=014 S11=070 S12=050 S13=000
S15=000 S19=000 S21=010 S22=017 S23=019 S25=005 S27=000
S28=008 S29=020 S30=000 S31=120 S32=002 S33=000 S34=000
S35=000 S36=014 S38=000 S39=000 S40=001 S41=000 S42=000

For "Integrated NPR Dial," the following settings need to be changed in the modem connect to the NPR:

  • Hyper-terminal Session, BAUD=9600, change to 19200
  • Change "&N6" to "&N10"
  • Change "&U6" to "&U10"
  • All other variables remain the same as shown
  • For 78051 Taps, use the “Remote Site Settings” and set up procedure.

 

Host Settings (This is the modem used at the workstation):

DIAL=TONE B0 E0 F0 M1 Q0 V0 X0 Y0
BAUD=9600 PARITY=N WORDLEN=8

&A0 &B1 &C1 &D2 &G0 &H0 &I0 &K0
&M4 &N0 &P0 &R1 &S0 &T5 &U0 &Y0

S00=001 S01=000 S02=043 S03=013 S04=010 S05=008 S06=002
S07=060 S08=002 S09=006 S10=014 S11=070 S12=050 S13=000
S15=000 S19=000 S21=010 S22=017 S23=019 S25=005 S27=000
S28=008 S29=020 S30=000 S31=120 S32=002 S33=000 S34=000
S35=000 S36=014 S38=000 S39=000 S40=001 S41=000 S42=000

For "Integrated NPR Dial," the following settings need to be changed in the modem connected to the PC or Workstation:

  • Hyper-terminal Session, recommend BAUD=9600, change to 19200
  • All other variables remain the same as shown
  • For Taps, use the "Remote Site Settings".; Do not use the "Host Settings"
Labels (1)
Labels:
  • TAC INET
Tags (1)
  • Find more articles tagged with:
  • 982
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore