Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

We Value Your Feedback!
Could you please spare a few minutes to share your thoughts on Cloud Connected vs On-Premise Services. Your feedback can help us shape the future of services.
Learn more about the survey or Click here to Launch the survey
Schneider Electric Services Innovation Team!

Spare stuffing box for valve V321

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Spare stuffing box for valve V321
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • SESA150559
    SESA150559
  • HenrikTarpgaard
    HenrikTarpgaard
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1183 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Spare stuffing box for valve V321

Picard Product_Support
‎2018-09-06 10:25 AM

Issue

Replacement stuffing box/stem seal

Environment

100108230

100108220

V321

100108210 

Cause

When leaking by the gland, a stuffing box replacement may sometimes help.

Resolution

The DN125 to DN150 of the V321 valve was changed around mid 2007 (the other sizes remained unchanged). With this change the valve stem changed from diameter 18mm to 12mm.

Unfortunately it was not thought to to update the data sheet in regards to the gland service kits – the gland service kit was updated by the factory for the new stem dia. but there was no advice as to servicing the old valve.

Fortunately the stuffing box from the V222 and V292 valves of DN125 to DN150 also fits the V321 valve, thus gland kit 100108210 should be the correct gland kit to use if you have the old valve (stem diameter of 18 mm).

If you have the new V321 model (stem diameter of 12 mm): Replacement/spare stuffing box for V321 DN65-DN100 is part no 100108220 and for DN125-150 it is part no 100108230.

The DN125 to DN150 of the V321 valve was changed around mid 2007, just before I started working for Schneider so I had to do some investigation here.
 
With this change the valve stem changed from dia. 18mm to dia.12mm
Unfortunately it was not thought to change the part numbers for the valve, nor to update the data sheet in regards to the gland service kits – the gland service kit was updated by the factory for the new stem dia. but there was no advice as to servicing the old valve.
Fortunately the gland kit from the V222 and V292 valves of DN125 to DN150 also fits the V321 valve.  Thus gland kit 1 001 0821 0 should be the correct gland kit to use.
The DN125 to DN150 of the V321 valve was changed around mid 2007, just before I started working for Schneider so I had to do some investigation here.
 
With this change the valve stem changed from dia. 18mm to dia.12mm
Unfortunately it was not thought to change the part numbers for the valve, nor to update the data sheet in regards to the gland service kits – the gland service kit was updated by the factory for the new stem dia. but there was no advice as to servicing the old valve.
Fortunately the gland kit from the V222 and V292 valves of DN125 to DN150 also fits the V321 valve.  Thus gland kit 1 001 0821 0 should be the correct gland kit to use.
With this change the valve stem changed from dia. 18mm to dia.12mm
Unfortunately it was not thought to change the part numbers for the valve, nor to update the data sheet in regards to the gland service kits – the gland service kit was updated by the factory for the new stem dia. but there was no advice as to servicing the old valve.
Fortunately the gland kit from the V222 and V292 valves of DN125 to DN150 also fits the V321 valve.  Thus gland kit 1 001 0821 0 should be the correct gland kit to use.
The DN125 to DN150 of the V321 valve was changed around mid 2007, just before I started working for Schneider so I had to do some investigation here.
The DN125 to DN150 of the V321 valve was changed around mid 2007, just before I started working for Schneider so I had to do some investigation here.
The DN125 to DN150 of the V321 valve was changed around mid 2007, just before I started working for Schneider so I had to do some investigation here.
 
 
 
Unfortunately it was not thought to change the part numbers for the valve, nor to update the data sheet in regards to the gland service kits – the gland service kit was updated by the factory for the new stem dia. but there was no advice as to servicing the old valve.
Unfortunately it was not thought to change the part numbers for the valve, nor to update the data sheet in regards to the gland service kits – the gland service kit was updated by the factory for the new stem dia. but there was no advice as to servicing the old valve.
Labels (1)
Labels:
  • Field Devices
Tags (1)
  • Find more articles tagged with:
  • 13201
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of