Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

SpaceLogic SLA CO2 sensors field calibration

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • SpaceLogic SLA CO2 sensors field calibration
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl
  • Brandon_Brouwer
    Brandon_Brouwer

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
2786 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

SpaceLogic SLA CO2 sensors field calibration

Brandon_Brouwer Explorer
‎2021-11-15 04:48 PM

on ‎2021-11-15 04:48 PM

Issue

SpaceLogic SLA CO2 units prior to date code 2138 cannot be field calibrated and ABC (Auto Baseline Calibration) is not set to ON by default.

Product Line

Field Devices

Environment

Veris Models – Cost Down version:

  • CWE2, CWE2C, CWE2D, CWE2H, CWE2K, CWE2M, CWE2N, CWV2
  • Firmware prior to REV1.05.23 Prior to 2138 DC

 

Schneider Electric + Veris Models:

  • CW2LA2A, CW2LA2AV, CW2LAXA, CW2LAXAV
  • SLABLC2, SLABLCV2, SLABLCVX, SLABLCX, SLASLC2, SLASLCV2, SLASLCVX, SLASLCX, SLAWLC2, SLAWLCV2, SLAWLCVX, SLAWLCX
  • Firmware prior to REV2.08.41 Prior to 2138 DC

Cause

The CO2 sensors are calibrated during manufacture, but can develop an offset during shipment or storage. Units cannot be field calibrated other than by the Auto Baseline Calibration (ABC) algorithm.  The offsets can be greater than 200PPM.  The ABC only calibrates at 30PPM a week.  That would require wait times of greater than 6 weeks.

Resolution

Replace with a unit with a date code of 2138 or higher or make sure ABC is enabled and wait the necessary time for ABC to correct.

Labels (2)
Labels:
  • EcoStruxure Building Operation
  • Field Devices
Tags (1)
  • Find more articles tagged with:
  • BrandonBrouwer21
Was this article helpful? Yes No
100% helpful (2/2)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.