SpaceLogic IP controllers may experience unexpected addition or loss of bindings to graphics and program logic.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • SpaceLogic IP controllers may experience unexpected addition or loss of bindings to graphics and program logic.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • GavinHe
    GavinHe

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
342 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

SpaceLogic IP controllers may experience unexpected addition or loss of bindings to graphics and program logic.

Sisko GavinHe Sisko
‎2025-10-14 03:44 PM

on ‎2025-10-14 03:44 PM

Issue

Bindings to graphics and programs on SpaceLogic IP controllers are being unexpectedly added or removed.

Product Line

EcoStruxure Building Operation

Environment

  • SpaceLogic IP Controller
  • Custom Types

Warning

Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support for assistance.

Cause

When a custom type is modified, a re-typing process is automatically triggered. The outcome of this process—specifically whether bindings are retained or lost—depends on the reference type used within the custom type.

Resolution

Care should be taken when designing custom types, as bindings within the type can be defined using one of three reference types: -

  • No Reference
  • Inner Reference
  • Outer Reference

Each reference type behaves differently during re-typing operations and can impact whether bindings are retained, added, or removed.  

 

When a custom type is modified or re-applied (e.g., attached to an object instance, version-changed, or undo check-out), a re-typing process is triggered. The behavior of bindings during this process depends on how they are defined in the custom type:

 

  1. No Bindings in Custom Type
    If the custom type does not contain any specific bindings, then during re-typing, existing bindings in the instance will be removed.
  2. Bindings Should Be Defined in the Custom Type
    To preserve bindings during re-typing, they should be explicitly added to the custom type using either:
    • Inner References
    • Outer References (with inner reference locked)
  1. Inner Reference Behavior
    If inner reference bindings are defined in the custom type, they will be automatically added to the instance during re-typing, even if they were not previously present.
  2. Outer Reference (Locked)
    Using outer references with inner reference locked ensures that bindings are preserved and not unintentionally modified during re-typing

For more detailed information on the re-typing process and reference behavior, please refer to the Re-Type section in WebHelp.

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (1)
  • Find more articles tagged with:
  • GavinHeward25
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore