- Issue
Panel showing detector Calibration error.
Product Line
ESMI Fire Detection.
Environment
- FFSULH1001.
- FFSULH1002.
Cause
When the contamination increases significantly and exceeds the sensitivity range for the smoke sensor, it is no longer able to perform calibration, causing a calibration error.
Resolution
- Understanding the Calibration Process:
- The Esmi Ultima panel performs daily calibration and drift compensation for all addressable smoke sensors at 7 AM by default.
 
- Sensitivity and Contamination:
- Over time, dust and other contaminants can build up in the chamber of a smoke sensor, increasing its sensitivity.
- Illustration:
- Left Image: Clean sensor requiring 2.0% per foot of smoke to activate the fire alarm.
 Right Image: Contaminated sensor with increased sensitivity, requiring less smoke to reach the alarm threshold of 2.0% per foot.
 
- Left Image: Clean sensor requiring 2.0% per foot of smoke to activate the fire alarm.
 
- 
Trouble Condition: - 
When the panel can no longer compensate for the contamination, it indicates a trouble condition. 
- 
The Esmi Ultima panels can compensate for contamination build-up in addressable smoke detectors and addressable multi-criteria detectors. 
- 
Daily calibration offsets any contamination, ensuring each smoke detector remains within its UL Listed sensitivity range. 
 
- 
- 
Recommended Action: - 
Clean or replace the sensor with a new one of the same model. If you have a replacement in stock, replace it immediately. 
 
- 
 
       
		
			 
		
		
		
		
		
	
			 
		
			 
		
		
		
		
		
	
			