SmartX Sensor Device TGML component shows wrong cover

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • SmartX Sensor Device TGML component shows wrong cover
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2607 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

SmartX Sensor Device TGML component shows wrong cover

Administrator DavidFisher Administrator
‎2022-01-18 08:21 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:51 AM

blank-cover.png

Issue

TGML graphic uses the NAM Standards component to display a SmartX Sensor Device with a dynamic cover model. The graphic always shows a blank faceplate instead of the correct face - 3 buttons, LCD, or Touchscreen.

Product Line

EcoStruxure Building Operation

Environment

  • SmartX Sensor Device (Living Space Sensor/Room Unit Device)
  • NAM Standards Team Components TGML Library
  • TGML Graphic
  • Thermostat - SmartX Living Space Sensor - Dynamic AppRev1.02.05

Cause

A script running inside the graphic component is expecting a well-formatted string representing the cover model on the cover model input binding. If that data is not delivered properly, the component defaults to a blank cover.

Resolution

Verify that the proper component is being used based on Sensor Firmware.

  1. Verify the proper IP controller firmware is installed to meet compatibility with the Host Server and also contain desired features.
  2. Once a controller is upgraded and the sensor has had time to upgrade, check the Sensor - Properties - Basic Tab - Application Software version.
    1. If greater than or equal to 1.02.05, then use Thermostat - SmartX Living Space Sensor - Dynamic AppRev1.02.05
    2. Otherwise use Thermostat - SmartX Living Space Sensor - Dynamic

 

The TGML component should work as expected, but factors outside of the graphic can make it not work right.

  1. Click on the SmartX Sensor Device and look at Properties > Basic > Status Information > Cover model.
    1. Does that show a valid cover model (ex: SXWSCBXSELXX) or does it show ASCII gibberish?
    2. If showing nonsensical ASCII string, hotfix firmware is available to address this.
    3. Install firmware at or higher than 3.02.03.02109, which includes fix for Defect# 46054 and 47266 affecting the Cover Model

      SmartX IP Controller v3.02.03.02109 - Firmware Package File
      Release Date: 2021-Dec-19
      https://ecoxpert.se.com/search?documentUUID=6b61d413-5cf8-47c0-ac4d-135391d375bf&title=SmartX%20IP%2...

      Release Notes v3.02.03 - SmartX IP Controller Firmware
      Release Date: 2021-Dec-19
      https://ecoxpert.se.com/search?documentUUID=1e29da8d-cf49-418d-92e5-e022bc4f33c7&title=Release%20Not...
  2. If the Cover Model is populated with a proper value, a previous firmware upgrade may have caused string values to stop writing properly through the TGML binding. There are two different resolutions to try in this order:
    1. Restart the AS-P
    2. Delete the SmartX Sensor Device (be sure to select "Keep references") and add it back as a new object with the same name and address.

 

objects-window.png

The binding controlling the dynamic display of different cover models on the graphic can be overridden.

  1. Inside the TGML component are 3 groups named "3 Button," "LCD", and "Touchscreen." All are hidden.
  2. Find the proper face and change it to default to Visible.
  3. Find the Bind named "CoverModel" and delete the binding and script beneath it. This is what is responsible for auto-changing the cover and is no longer needed.
Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (1)
  • Find more articles tagged with:
  • DavidFisher22
Was this article helpful? Yes No
100% helpful (3/3)

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of