Issue
Attempting to connect with SmartStruxure Building Operation Workstation to an Automation Server results in a crash report.
A problem occurred in this application
Environment
SmartStruxure Building Operation 1.3.0 SP1 - 1.3.0.10100
Windows 7 64 bit
Cause
Temporary user files result in a conflict between the user files and the server you are connecting to.
Resolution
Browse to the user application settings.
C:\users\[username]\AppData\Roaming\Schneider Electric\Workstation\1.3.0.10100
Delete the contents of this folder and start Building Operation Workstation again to connect to the server.