Issue
Site Access Control lockdown for the entire complex. But, also allow certain cards to override certain doors during an emergency situation.
Environment
I/NET site with access control
Cause
There is a requirement to lockdown an entire complex with a single toggle switch, but allow First Responders access to certain locked doors in the building.
Resolution
There are two different Demo programs for this process
-
One Link program (Download One Link Zip file):
- MCI -- 7798
- DPU – SCU1284 (2 addresses)
-
A maintained switch SPDT
-
Two or more Links program (Download Two Link Zip file)
- MCI – 7798 Link1
- MCI – 7793 Link2 – Channel “B”
- SCU1284 (2address) Link1
- SCU1284 (2address) Link2 – On second channel
- A maintained switch SPDT
Each of the above zip files have the following inside:
Note: This would be restored to your test bench, and then configuration implemented into a production site.