Single-pushbutton, Dual-pushbutton and Latched Lighting Zones
  • Single-pushbutton, Dual-pushbutton and Latched Lighting Zones
‎2018-09-06 03:29 PM
What is the difference between Single-pushbutton, dual-pushbutton and latched in a lighting zone?
  • I/NET Seven
  • Lighting Zone Controller
Programming lighting controls offers zone options for after hours override.
  • Single-pushbutton is used when a momentary spring-loaded button is required.
    1. You push a button and a closed contact (1) is made.
    2. Releasing the button results in a open contact (0) and starts the zone.
  • Dual-pushbutton is a two button switch.
    1. Pressing one button gives you a closed contact (1).
    2. Pressing another button results in a closed contact (0) on the second input and the zone is turned off.
  • Latched is for when you have a light switch.
    1. Flip a switch and it stays on (1).
    2. Flip it the other way (0) and it turns off.
  • TAC INET
  • 950