Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Sigma Log Data Recording Every 15 Minutes Synchronized to the Hour

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Sigma Log Data Recording Every 15 Minutes Synchronized to the Hour
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl
  • sesa139513
    sesa139513
  • RogerHa
    RogerHa
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1099 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Sigma Log Data Recording Every 15 Minutes Synchronized to the Hour

Picard Product_Support
‎2018-09-06 10:19 AM

Last Updated: Administrator CraigEl Administrator ‎2025-10-21 08:16 PM

Issue

A utility is being used to record Sigma log data and store it in the cloud. There is a requirement for log timestamps to occur every 15 minutes, precisely synchronized to the hour (e.g., 00:00, 00:15, 00:30, 00:45).

Product Line

Satchwell BAS & Sigma

Environment

Satchwell Sigma

Cause

Sigma does not provide a native mechanism to define the exact start time for a log set. When configured to log at timed intervals, the log bucket file is downloaded to the controller and begins processing from that moment—resulting in unsynchronized timestamps.

Resolution

An engineering workaround can be implemented to achieve synchronized 15-minute logging. This involves using a program point for each value that needs to be logged.

Sample Program Code

10 XFlo = POINT 0|41  ; Object to be logged
20 IF MINUTE = 0 OR MINUTE = 15 OR MINUTE = 30 OR MINUTE = 45 THEN GOTO 40
30 RETURN VIA TEXT 92 VALUE YFlo
40 IF SECOND DOWN THEN GOTO 60
50 RETURN VIA TEXT 92 VALUE YFlo
60 YFlo = XFlo
70 RETURN VIA TEXT 92 VALUE YFlo

Instructions

  1. Replace POINT 0|41 with the actual object reference you wish to log.
  2. Configure the log set to use "Change of Value" as the logging trigger.
  3. Ensure each required value has its own program point using the logic above.

Additional Notes

  • This method ensures that values are captured exactly at 15-minute intervals aligned with the hour.
  • It is particularly useful when integrating with external systems or cloud-based analytics that rely on consistent timestamping.
Labels (1)
Labels:
  • Satchwell BAS & Sigma
Tags (3)
  • Find more articles tagged with:
  • 13522
  • CraigEllis25
  • hourly
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore