Issue
Duplicated SFE Short Form Edit graphics
Product Line
EcoStruxure Building Operation
Environment
- Building Operation Enterprise Server
- Sigma
Cause
A duplicated set of Short Form Edit graphics are created but are in a different language appear along side the original SFE graphics when using Data Import with a Sigma transition into EBO
The example below shows the original DataImport was completed in English, the second DataImport was completed in Danish.
Resolution
Before a Sigma DataImport is undertaken, ensure that the correct language is set in EBO.
Delete the Sigma Interface, set the correct language and start the transition again.