Sigma - Site requirement to control five chillers in sequence.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Sigma - Site requirement to control five chillers in sequence.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1431 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Sigma - Site requirement to control five chillers in sequence.

Picard Product_Support
‎2018-09-06 01:24 PM

Last Updated: Crewman ContentModerator ‎2025-08-11 04:06 AM

Issue

Assistance is required to create this programme.

Environment

  • Sigma
  • Programme
  • Chiller control
  • Prog points

Cause

This programme has been attempted, but does not operate as required.

Resolution

The programme must control 5 chillers in a fixed sequence.

There must be a delay of 20 minutes between starting chillers, (configurable).

The temperature differential from zero to all chillers operating must be adjustable.

The suggested programme is as follows:

10 XFlo = POINT 0|144 - POINT 0|140
20 IF XFlo <= 0.000000 THEN XFlo = 0.000000
30 IF XFlo >= POINT 0|141 THEN XFlo = POINT 0|141
40 XFlo = ( XFlo / POINT 0|141 ) * 100.000
50 XInt = 0
60 IF XFlo >= 20.0000 THEN XInt = XInt + 1
70 IF XFlo >= 40.0000 AND YInt >= 1 THEN XInt = XInt + 1
80 IF XFlo >= 60.0000 AND YInt >= 2 THEN XInt = XInt + 1
90 IF XFlo >= 80.0000 AND YInt >= 3 THEN XInt = XInt + 1
100 IF XFlo >= 100.000 AND YInt >= 4 THEN XInt = XInt + 1
110 IF TIME LEFT THEN GOTO 180
120 IF XInt > YInt THEN GOTO 150
130 YInt = XInt
140 GOTO 190
150 ZInt = INT ( POINT 0|142 ) * 60.0000
160 SET TIMER ZInt
170 YInt = YInt + 1
180 IF XInt < YInt THEN SET TIMER 0
190 RETURN VIA TEXT 92 VALUE FLOAT ( YInt )

Objects:

  • 140 - SPA Object - Setpoint
  • 141 - SPA Object - Differential required - 0 chillers to 5 chillers (degrees over which all chillers switch on)
  • 142 - SPA Object - Delay time in minutes required.
  • 144 - AI Object - Chillers Return Temperature

Link this programmable object to the chiller commands, using the hysteresis option.

On each chiller command object, enable the hysteresis option, setting will be as below.

  • Chiller 1 -  hysteresis low setting  0.1 and high setting  0.9.
  • Chiller 2 -  hysteresis low setting  1.1 and high setting  1.9.
  • Chiller 3 -  hysteresis low setting  2.1 and high setting  2.9.
  • Chiller 4 -  hysteresis low setting  3.1 and high setting  3.9.
  • Chiller 5 -  hysteresis low setting  4.1 and high setting  4.9.

For a copy of the above text, click here.

Labels (1)
Labels:
  • Satchwell BAS & Sigma
Attachments
Tags (1)
  • Find more articles tagged with:
  • 6213
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of