Issue
Lon values on the Sigma IC-LON controller intermittently go into and out of default, causing unreliable data communication.
Product Line
Satchwell BAS & Sigma
Environment
- Satchwell Sigma IC-LON
- Satchwell Sigma IC3-LON
Cause
This behavior is typically due to mismatched heartbeat settings between the IC-LON controller and the field controller.
Resolution
-
Check Heartbeat Settings:
- Locate the
gateway.txtfile on the IC-LON controller. - Compare the receive heartbeat setting in this file to the send heartbeat setting of the field controller.
- Locate the
-
Recommended Configuration:
- Set the receive heartbeat to 2–5 times the send heartbeat.
- Start with 2× and increase incrementally if the issue persists.
-
Special Case – No Heartbeat & Rare Value Changes:
- If the field controller does not send a heartbeat and the LON value changes infrequently:
- Disable the receiver heartbeat in the IC-LON’s
gateway.txtfile by setting the heartbeat value to0.
- Disable the receiver heartbeat in the IC-LON’s
Example Configuration:
2, 2, 112, 1293, 0, 0, 0 - If the field controller does not send a heartbeat and the LON value changes infrequently:
Additional Notes
- The Sigma system is no longer supported. Consider transitioning to EcoStruxure Building Operation for continued support and enhanced functionality.