Issue
Troubleshooting Sigma IC LON Values going on and offline
Product Line
Satchwell Sigma
Environment
- Sigma Release 4_05-SEB (Build 3_43_18)
- Sigma Release 4_05-SP2 (Build 3_42_48)
- Sigma Release 4_06 (Build 3_44_14)
- Sigma Release 4_06 SP1 (Build 3_44_16)
- Sigma Release 4_07 (Build 3_45_48)
- Sigma Release 4_07-SP1 (Build 3_45_51)
- Sigma Release 4_07-SP2 (Build 3_45_58)
- Sigma Release 4_08 (Build 3_46_57)
- IC LON
Cause
Lon Values going into and out of default
Resolution
- Compare the IC-LON’s Receive heartbeat set in the “gateway.txt” file in the IC-LON controller, to the send heartbeat set in the controller.
The recommendation is for the receive heartbeat be set to 2-5 times the send heartbeat of the field controller.
Starting at 2 times, then increasing if the problem persists. - If the controller doesn’t have a heartbeat and the LON value rarely changes, disable the receiver heartbeat in the IC-LON’s gateway.txt file by setting the heartbeat to 0.
Example:
1 2 3 4 5 6 7
2, 2, 112, 1293, 0, 0, 0
The Sigma system is now out of its support period, consideration should be given to transitioning or upgrading to
SpaceLogic - EcoStruxure Building Operation.