Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Sigma - How does a UNC controller handle log data when comms to the server has failed.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Sigma - How does a UNC controller handle log data when comms to the server has failed.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RogerHa
    RogerHa
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1223 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Sigma - How does a UNC controller handle log data when comms to the server has failed.

Picard Product_Support
‎2018-09-06 12:14 PM

Issue

This article clarifies what a Sigma UNC controller does when logging is going on and comms to the server has been lost.

Environment

Sigma - All versions

Cause

When a sigma controller is logging, during normal operation the data is uploaded to the logging database at various intervals. These uploads are generally controlled by the UNC controller. If comms to the server is lost then the data is stored in RAM until comms to the server is re-established. The resolution details how this happens and what the limitations are.

Resolution

In the controller, after all files have been downloaded, the Alarm buffer is created. The Alarm buffer holds the queue of alarms and logs being sent to the server and can hold up to 500 entries.

Then memory is allocated to the Logging buffer which stores partially complete logging data. It is allocated memory as follows:

 

First series controllers (532, 496/596, IC1):

75% of the remaining memory

ARM 7 series controllers (632, 696/796, IC3):

512kB

 

The Logging buffer contains 138-byte Tracks with one Track for each logged object. Log records are added to the Track as they occur and the Track is transferred to the Alarm buffer when full.

The maximum number of log records that a Track contains depends on the type of object and the type of log as follows:

 

Operation

Object Type

Records per track

Timed

Analogue

25

Timed

Digital

100

Event

Analogue

14

Event

Digital

32

Alarm/report (as a log)

Any

28

 

Partially full Tracks can be moved to the Alarm buffer (and thus automatically to the server) by selecting Diagnostics > Options > Retrieve Logs.

Where an Autodial connection is used, a telephone call is initiated when any alarm (non opportunistic) or log is placed in the Alarm buffer.

Labels (1)
Labels:
  • Satchwell BAS & Sigma
Tags (1)
  • Find more articles tagged with:
  • 8131
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of