Sigma 4.08, Access Class 17 to 32 do not display object values
  • Sigma 4.08, Access Class 17 to 32 do not display object values
  • DavidChild
    DavidChild
‎2018-09-06 09:05 AM
Sigma 4.08
In Sigma 4.08 Build 3.46.57, if an Index or Object is assigned an Access Class of 17 to 32. The object does not display a value.
Request Hot Fix 3.46.86 from Product Support Services.
The Hot Fix will need to be installed at each local and remote client.
When the Hot Fix is deployed, each object that has been assigned an Access Class of 17 to 32 will need to be opened in Object Editor, exit, saved and finally downloaded to the controller. Single object download without opening in Object Editor or Point File download is not sufficient.
  • Satchwell BAS & Sigma
  • 17713