Should the Modbus master (eg Xenta 913) also be terminated if it is in the middle of the Modbus bus?
  • Should the Modbus master (eg Xenta 913) also be terminated if it is in the middle of the Modbus bus?
  • sesa177673
    sesa177673
‎2018-09-10 08:32 AM
  • Xenta Server with Modbus capabilities
  • Xenta 511, 527, 701, 711, 721, 731, 913
There are a number of installation possibilities/restrictions that may mean that the Modbus master does not always end up at one of the ends of the communication field bus.
Only the ends of the bus should be terminated (see below).
More information is available for Modbus.org at the following link:
Modbus over serial line specification and implementation guide V1.02.
  • 7172