Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

We Value Your Feedback!
Could you please spare a few minutes to share your thoughts on Cloud Connected vs On-Premise Services. Your feedback can help us shape the future of services.
Learn more about the survey or Click here to Launch the survey
Schneider Electric Services Innovation Team!

Setting up an AIC (Access Initiated Control) to turn on an AHU or other systems

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Setting up an AIC (Access Initiated Control) to turn on an AHU or other systems
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Tom_Poovey
    Tom_Poovey
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1423 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Setting up an AIC (Access Initiated Control) to turn on an AHU or other systems

Picard Product_Support
‎2018-09-07 12:38 AM

Last Updated: Administrator DavidFisher Administrator ‎2020-10-25 10:57 AM

Issue

Setting up an AIC (Access Initiated Control) to turn on an AHU or other systems

Product Line

TAC INET

Environment

  • Access Initiated Controls
  • Event Sequence

Cause

Access Initiated Controls are used to fire a DO on any entry or exit event from the security system. This can be used to accomplish just about any sequence of events, but it most commonly used for after hours enabling of HVAC equipment upon badging in.

Resolution

  1. Define all the points in the database. Then choose one as the AIC Trigger point and define an "Event Definition" on that point
    residentiopoint.png

     

  2. This is how the "Event Definition" looks
    eventdefinition.png

     

  3. Close out of the Controller Summary and Select Edit>Controller>Event Sequences
  4. Create a New event sequence.
  5.  Since the AIC Trigger is also an external point that starts the AHU you do not have to start that point. However, you have to stop that point. In my example here the AIC runs the points for 3600 seconds and stops the AHU followed 5 seconds later stopping each of the Floor Lights. If the AIC Trigger were an internal DO, you would need to also trigger the AHU S/S
    eventsequence.png

     

  6. Once you have programmed your Event Sequence, you can test it by manually triggering the DO point.
  7. When everything works correctly, select Edit>Controller>Access Initiated Control
  8. Create a new AIC
  9. You will notice the Trigger point is the AHU S/S (DO). This DO is triggered from a Reader Entry by a valid card
    modify-aic.png

     

  10. This is where you define which door reader the AIC is triggered from. If desired, you can have several doors such as all perimeter doors trigger the AIC.
    aicdoors.png

     

  11. This is where you select which person is allowed to trigger the AIC with their card read. In this example the only person allowed to trigger the AIC is Fred Flintstone. You can also select the "All individuals in Range" checkbox in the AIC editor to allow all individuals from a specific tenant to trigger this AIC.
    aicafterhrs.png

     

  12. Once you have created the AIC you can test your programming. Remember that the AIC piece is only supposed to trigger the DO and the event sequence will actually turn everything else off or on.
Labels (1)
Labels:
  • TAC INET
Tags (2)
  • Find more articles tagged with:
  • 2503
  • aic
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of