Setting up a Modbus, M-Bus or BACnet communications log in a Xenta 5/7/9xx

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Setting up a Modbus, M-Bus or BACnet communications log in a Xenta 5/7/9xx
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • HenrikTarpgaard
    HenrikTarpgaard
  • Anonymous user
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3034 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Setting up a Modbus, M-Bus or BACnet communications log in a Xenta 5/7/9xx

Picard Product_Support
‎2018-09-07 05:18 AM

Issue

Configuration instructions for setting up a communications VX Log in the Xenta 5/7/9xx for communications troubleshooting.

Environment

  • Xenta Servers
  • Xenta 511, 527, 555, 701, 711, 721, 731, 913
  • VXI

Cause

Configuration instructions for setting up a communications log in the Xenta 5/7/9xx for communications troubleshooting. Obtaining the communications log for a Modbus or BACnet network is crucial in finding communications errors, or other unforeseen problems with integrating to third party devices.

Resolution

Step by step instructions for creating the communication log for troubleshooting or for data analysis:

  1. Log In to the Xenta 5/7/9xx controller and navigate to the Utilities Folder:


     
  2. Click on the Target System Folder and choose VXI Web Shell Commands:


     
  3. The command line should appear with VX populated in the command line:


     
  4. Logging to file in the Xenta controller will first need to be enabled to by typing VX L 1 and press submit:


     
  5. VXI Web Shell Commands should return a messing indicating logging has been enabled for 1 hour:


     
  6. After logging has been enabled, the verbosity will need to be set in order to capture each layer of communications on the wire. In the command line type VX V 9 and press submit:


     
  7. VXI Web Shell Commands should return a messing indicating the verbosity has been set to 9 and what messages you will see with this verbosity level :


     
  8. Let the communications log run for 5-10 minutes. Create as many changes on the 3rd party wire as possible to get various data changes to and from the Xenta Server.
     
  9. In the command line type VX O and press submit:


     
  10. This command will output the communications log the Xenta Server has collected. Highlight this entire output log and copy, then paste it into notepad for archiving or emailing:


     

To set the communication logging back to default type "vx V 1" or power cycle the Xenta Controller.

To stop the logging to file, type "vx L".

 

For TCP/IP logging you can only monitor one client at a time:

  1. Complete Steps 1- 8 above
  2. Enter "vx d"
  3. This will display a list of the TCP available devices
  4. Enter vx d # where # is the number corresponding to the deice you wish to monitor
  5. To view the log, follow steps 9 and 10 above
Labels (3)
Labels:
  • Satchwell MicroNet
  • TAC INET
  • TAC Vista
Tags (2)
  • Find more articles tagged with:
  • 4462
  • PeterLarsen21
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore