Setting a TAC Xenta OP to show IP (US) units instead of SI units
TAC Vista
Xenta OP
Switching the TAC Xenta OP between imperial and metric units.
  1. Connect to a TAC Xenta 100
  2. After pressing "down," there is a setting "unit as"
  3. Toggle between SI and US (IP) by pressing the "up" button
Please note that this only changes the presentation, and that both absolute as well as relative values are re-calculated. This means that a difference in temperature may be shown incorrectly.