Setpoint in TAC Xenta OP can't be changed to Value above 100
  • Setpoint in TAC Xenta OP can't be changed to Value above 100
  • MikaelKrantz
    MikaelKrantz
  • PeterEdvik
    PeterEdvik
  • sesa145087_brid
    sesa145087_brid
‎2018-09-07 07:11 AM
Setpoint in TAC Xenta OP can't be changed to a value above 100. Workstation does not have this limitation.
TAC Vista
  • Vista Workstation
  • Vista Server
  • Xenta OP
The default changing range of an analog value in the TAC Xenta OP is from 0 to 99.9. If the value needs to be changed beyond this range, the default property needs to be modified.
In TAC Menta, click Tools, OP Configuration, to open the OP configuration window. Navigate to the value that needs to be changed, and choose property. Modify the minimum and maximum value of this value. Then this value can be changed in the TAC Xenta OP freely.