Issue
Setpoint in TAC Xenta OP can't be changed to a value above 100. Workstation does not have this limitation.
Product Line
TAC Vista
Environment
- Vista Workstation
- Vista Server
- Xenta OP
Cause
The default changing range of an analog value in the TAC Xenta OP is from 0 to 99.9. If the value needs to be changed beyond this range, the default property needs to be modified.
Resolution
In TAC Menta, click Tools, OP Configuration, to open the OP configuration window. Navigate to the va...