Can a UNC be setup as a BACnet server to expose its native Niagara objects as BACnet objects?
TAC IA Series
  • Niagara R2
  • UNC-520
By default, the UNC can only act as a BACnet client, not as a BACnet Server. A UNC-520 can be configured as a BACnet Server.
Steps for configuring exposing native Niagara objects and BACnet objects:
  1. Open the properties of the native Niagara object you want to expose as a BACnet object.
  2. Click on its Config tab
  3. The foreignAddress must be changed from its default of “-1” to an integer from 0 - 4194302. (BACnet instance number rules applies)
  4. Apply the change
The object is now exposed as a BACnet object.
The following standard Niagara objects can be exposed and BACnet objects:
  • AnalogInput (AI)
  • AnalogOutput (AO)
  • BinaryInput (BI)
  • BinaryOutput (BO)
  • MultistateInput (MSI)
  • MultistateOutput (MSO)
  • Calendar
  • Schedule
Reference Chapter 4 of the "BACnet Integration Reference" guide for more detailed information.