Set up a MR-VAV-AX (ASC) as Standalone

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Set up a MR-VAV-AX (ASC) as Standalone
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
2347 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Set up a MR-VAV-AX (ASC) as Standalone

Picard Product_Support
‎2018-09-06 09:24 PM

Last Updated: Administrator DavidFisher Administrator ‎2020-08-18 06:52 AM

Issue

Set up a MR-VAV-AX (ASC) as Standalone

Product Line

TAC INET

Environment

MR-VAV-AX

Cause

Air balance must be done to calibrate the airflow sensor on the MR-VAV-AX.

Resolution

Download Tech Tip 072

 

Equipment:

Air Balancing Hood or Manometer and Digital Thermometer.

 

Assumptions:

  • The MR is powered up.
  • An I/STAT, or an M/STAT is plugged into the service port of a S/STAT or W/STAT, which is plugged into the MR-VAV-AX.
  • The AHU is running.
  • The Space sensor is installed.
  • The Duct static pressure is constant.
  • The dip switches are set properly for the desired VAV configuration. (See TCON 147)
  • You have a Pocket Reference Card (TCON 149).
  • You are familiar with the use and operation of the I/STAT / M/STAT with respect to navigating the Service mode to various mnemonics’ menus. (See TCON 147)

 

Initial Setup

You should notice that two things have already happened:

  1. The MR is in the unoccupied mode.
  2. The setpoint adjust has defaulted to "-5", making the setpoint display appear low.

For the MR to work in a Standalone mode the use of an off-board time clock for the occupied and unoccupied times is recommended. It should be connected to the "Local Occ" point(TB5 input #2 to TB5 ground.) The "Occ" mnemonic under Unit Parameters must be set to ONE for the "Local Occ" point to be used. If the MRs are to be left in the occupied mode indefinitely, install a jumper across the "Local Occ" point instead of using the time clock contacts. Connect the jumper to (TB5 input #2 to TB5 ground.) Using the I/STAT or M/STAT go to Set Temp and increase the value by 5°. This will get the Setpoint Adj. back to zero.

 

"Cooling Low Flow" (CLF - min. CFM) and "Cooling High Flow" (CHF - max. CFM) Setup

  1. Put the I/STAT or M/STAT into the Service Mode.
  2. Go to "AP", select "CLF", (the value displayed is "multiplied by" 1000 so 0.24 is 240). Enter the minimum CFM by using the arrow keys to position the LED for the digit to be changed and enter the value by using the "+" and "-" keys. Notice the decimal position will not move. You are entering the value "multiplied by" 1000. Refer to the Pocket Reference Card (TCON 149), paragraph 5.
  3. Usually the minimum air flow value can be found on the Mechanical box schedule drawings. The lowest reading that the ASC’s sensor can sense is about .03" to .05" of Water Column(W.C.) Therefore, the "CLF" must be set above this level. If the ASC is required to control in that range, it will tend to oscillate.
  4. Select "CHF" and enter the maximum CFM for this box at 1" W.C., this can be found on the DeltaP to CFM graph that is associated with this VAV box’s pickup device, or the box schedule may also provide the maximum cfm value.

 

Central Plant Heat "Heating Low Flow" (HLF) and "Heating High Flow" (HHF) Setup

  • Use only if Central Plant Heat is required and setup Unit Parameter’s(UP) CPH set to "1".
  • An open contact at Input 3 will indicate that the Central Plant Heat mode is on. A closed contact indicates CPH is off.
  • Using the procedure described above for "CLF" and "CHF" instead select "HLF" and "HHF" and enter the desired Low and High Flow CFM values for the Heating Mode. Otherwise go to the next section.
  • NOTE: If you have a auxiliary stage of heat, it will not be energized unless the CFM input is reading at least 80% of the "HLF" setting.

 

Calibrate the flow pickup:

  1. Go to Unit Parameter "UP", select "dd" (duct diameter).
  2. Enter the duct diameter this will enable the MR to calculate the Pickup Factor "PF" for us.
    NOTE: It is recommended that you begin with the value provided by the VAV Manufacturer for the pickup factor. Then calibrate if necessary using the following procedure.
  3. Go to "AP", select "PPF" (pickup factor calibration).
  4. The MR will drive the box open and modulate the damper to maintain the "CHF" level. This may take 5 - 10 minutes.
    NOTE: The stroke time is defined using the Damper Stroke (ds) parameter. The ASC provides several means of synchronizing the point with the physical damper position.
    1. 1. When this point is controlled to a value of 0, the decrease pulse will be on for 125% of the damper stroke.
    2. 2. When this point is controlled to a value of 100, the increase pulse will be on for 125% of the damper stroke.
    3. 3. When the damper stroke duration is modified, the decrease pulse will be on for 125% of the damper stroke.
    4. 4. When the power is cycled on the ASC, the decrease pulse will be on for 125% of the damper stroke.
    5. 5. Any time the ASC is the target of an Update_ASC or a Copy_Parms, the decrease pulse will be on for 125% of the damper stroke.
  5. After the reading has settled out, take a reading with a Hood or Manometer, which has been setup, and measure the actual CFM and enter that value now into the I/STAT-M/STAT using the Select and change buttons.
  6. The software has entered a unique Pick-up Factor "PF" in the MR for this box.

 

Calibrate space temperature (if necessary):

  1. To calibrate the Space Sensor while in the Service Mode, go to "oP" Operational Parameters.
  2. Select "CSS" (calibrate space sensor).
  3. Measure the actual temperature with a digital thermometer and enter the value.
  4. If your box has no heat or has a fan with electric heat. You’re finished. Go to the next box.

 

Hot water coil:

  1. If you have a hot water valve on your box and the stroke time is not 600 seconds:
  2. Go to "UP" (Unit Parameters) and select "Ho", Heating Output. Select1 for 1-OutPWM, 2 for 2 Out-PWM(Floating), or 3 for Duty Cycle 1 output.
  3. Go to "UP" Unit Parameters and select "HS" (heating stroke) and enter the actual stroke time in seconds.

 

Air Balance:

If you require closely calibrated CFM readings proceed with the following steps:

  1. Go to "AP" (Airflow Parameters)
  2. Select "CPL" (calibrate low flow) and the damper will begin to close.
  3. Remember, the damper motor may take 3 minutes to get to the Cooling Low Flow setpoint.
  4. With a Hood, measure the total air flow and enter the measured CFM value.
  5. Select "CPH" (calibrate high flow).
  6. The damper will drive open to the Cooling High Flow setpoint. (remember the damper motor has a 185 sec stroke).
  7. When the reading stabilizes, take your measured CFM reading and enter it now. This procedure will de-calibrate the CFM input from the 0-1"readings to compensate for box, pickup, or hood irregularities/errors.

Caution: When the decision is made to connect the MR-VAV-AX to a MRI or MCI please note the following: Avoid updating the MCI or ASC after initial setup as this will delete any MCI resident calculations, ATS, etc. that you may have added off-line that are residing at the same point addresses that the MR-VAV-AX is using. There are a variety of box types and a variety of other things that can be change if your application requires it. (Refer to TCON147)

Labels (1)
Labels:
  • TAC INET
Attachments
Tags (1)
  • Find more articles tagged with:
  • 1086
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of