Issue
A Xenta 102-AX accepts a 0-5V input on all external inputs. If Universal Input 3 is designated as CO2, the range of the input needs to match the range of the sensor.
Product Line
EcoStruxure Building Operation, TAC Vista
Environment
- Xenta 102-AX
- Universal Input 3
- CO2 sensor
Cause
The default setting (a gain of 1/1) results in
- 0V = 0ppm
- 5V = 1023ppm
(1023 is a resolution of the onboard analog to digital converter.)
Resolution
Refer to page 3-66 of the TAC Xenta 102-AX Software & Hardware Manual for more detail.
- Calculate the required gain for the range of the CO2 sensor.
- Ensure the sensor outputs a 0-5V signal.
- Note the CO2 level at 5V. In this example, 2000ppm.
- Divide the maximum CO2 reading by the analog to digital converter bit resolution (1023).
- Multiply the result by 1000.
- (2000 / 1023) * 1000 = 1955
- Locate the value for Universal Input 3 SCPTgain. There are four locations to alter this value:
- Xenta 102-AX Plug-in
Go to the Browser Tab > Xenta102AX > UnivIn3 Sense > SCPTgain > multiplier. Over on the right, enter in 1955/1000 and hit Set Value. - LonMaker or LNS browser
Open the browser window by right clicking on the 102-AX in the drawing and selecting Browser. Look in the Functional Block column for UnivIn3Sense. In that category is a point called SCPTgain. Click on it and then enter up top 1955/1000. Hit the red down arrow to download the value to the device. Enable monitoring on the nvoCO2sensor value or reopen the browser to view the new CO2 value. - Vista Workstation
Go to the 102-AX.UnivIn3_Sense module and locate the SCPTgain point. Double click it. By Multiplier enter 1955 and by Divisor enter 1000. - StruxureWare WorkStation
Go to the 102-AX and click on UnivIn3Sense module and in the Variables tab locate the nciGainUIx point and expand it. For Multiplier, enter 1955 and save. For Divisor, enter 1000 and save.
- Xenta 102-AX Plug-in