Set the range of a Xenta 102-AX CO2 sensor

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Set the range of a Xenta 102-AX CO2 sensor
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1996 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Set the range of a Xenta 102-AX CO2 sensor

Picard Product_Support
‎2018-09-07 04:00 AM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:58 AM

Issue

A Xenta 102-AX accepts a 0-5V input on all external inputs. If Universal Input 3 is designated as CO2, the range of the input needs to match the range of the sensor.

Product Line

EcoStruxure Building Operation, TAC Vista

Environment

  • Xenta 102-AX
  • Universal Input 3
  • CO2 sensor

Cause

The default setting (a gain of 1/1) results in

  • 0V = 0ppm
  • 5V = 1023ppm

(1023 is a resolution of the onboard analog to digital converter.)

Resolution

Refer to page 3-66 of the TAC Xenta 102-AX Software & Hardware Manual for more detail.

  1. Calculate the required gain for the range of the CO2 sensor.
    1. Ensure the sensor outputs a 0-5V signal.
    2. Note the CO2 level at 5V. In this example, 2000ppm.
    3. Divide the maximum CO2 reading by the analog to digital converter bit resolution (1023).
    4. Multiply the result by 1000.
    5. (2000 / 1023) * 1000 = 1955
  2. Locate the value for Universal Input 3 SCPTgain. There are four locations to alter this value:
    1. Xenta 102-AX Plug-in
      Go to the Browser Tab > Xenta102AX > UnivIn3 Sense > SCPTgain > multiplier. Over on the right, enter in 1955/1000 and hit Set Value.
    2. LonMaker or LNS browser
      Open the browser window by right clicking on the 102-AX in the drawing and selecting Browser. Look in the Functional Block column for UnivIn3Sense. In that category is a point called SCPTgain. Click on it and then enter up top 1955/1000. Hit the red down arrow to download the value to the device. Enable monitoring on the nvoCO2sensor value or reopen the browser to view the new CO2 value.
    3. Vista Workstation
      Go to the 102-AX.UnivIn3_Sense module and locate the SCPTgain point. Double click it. By Multiplier enter 1955 and by Divisor enter 1000.
    4. StruxureWare WorkStation
      Go to the 102-AX and click on UnivIn3Sense module and in the Variables tab locate the nciGainUIx point and expand it. For Multiplier, enter 1955 and save. For Divisor, enter 1000 and save.
Labels (2)
Labels:
  • EcoStruxure Building Operation
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 4304
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore