Sensors for Clean Room, Swimming Pool, Outdoor Temperature, Explosion Proof, and Color

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Sensors for Clean Room, Swimming Pool, Outdoor Temperature, Explosion Proof, and Color
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
5703 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Sensors for Clean Room, Swimming Pool, Outdoor Temperature, Explosion Proof, and Color

Picard Product_Support
‎2018-09-10 12:44 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 04:00 AM

Issue

What sensors can be used in Clean Rooms 

What sensors can be used outdoors for temperature measurement

What sensor can be used in a swimming pool

What sensor would be explosive proof

What color is the wall sensor and are custom colors available

Environment

Building Automation System such as I/NET, Vista, or Continuum at a site containing a clean room, swimming pool, or outdoors

Cause

Questions concerning the uses of Schneider Electric sensors in Clean Room applications

Questions concerning temperature sensors for Outdoor installations

Questions concerning temperature sensors for swimming pools

Questions concerning explosion proof sensors*

Questions concerning color and custom colors for sensors

Resolution

All the Schneider Electric temperature sensors found in the HVAC Sensor Catalogue as well as on iPortal provide high accuracy and can be mounted on the wall, in ducts, or in a J-Box. Appendix A provides the accuracy for each of the temperature sensors.

Color: STR series wall sensors are:
Front Cover: White NCS S-0500 N
Core Plate: White NCS S-0500 N and Gray NCS S-2500 N
Base Plate: Gray NCS S 1502-R
Manufacturing in custom colors in not available. One option could possibly to have the sensors locally custom finished to meet customer's requirements.
While there is not a direct cross reference to RAL colors, our engineering team has found the closest alternates. Please see the attached pdf.

Clean Room: Depending on the specified limits of the clean room, the variety of sensors offered by Schneider Electric are possible solutions. Thing you may want to research are the standards required for the site. Clean rooms are a controlled environment where products are manufactured. It is a room in which the concentration of airborne particles is controlled to specified limits. Eliminating sub-micron airborne contamination is really a process of control. These contaminants are generated by people, process, facilities and equipment and must be continually removed from the air. The level to which these particles need to be removed depends upon the standards required.

The most frequently used standard is the ISO 14644 Standards, which were first formed from the US Federal Standard 209E Airborne Particulate Cleanliness Classes in Cleanrooms and Clean Zones.  ISO 14644 is a document that establishes standard classes of air cleanliness for airborne particulate levels in cleanrooms and clean zones. Strict rules and procedures are followed to prevent contamination of the manufactured product.

The only way to control contamination is to control the total environment. Air flow rates and direction, pressurization, temperature, humidity and specialized filtration all need to be tightly controlled.

Outdoor:  Schneider Electrics selection of Outdoor Temperature Sensors are the STO100, 200, 500, & 600. These outdoor sensors are intended for outdoor wall mounting. Variants are available for Vista, I/NET, Continuum and Satchwell systems. The body has a 20mm conduit entry and the product is supplied with a conduit gland.

Range -40 to +90 °C
Accuracy See Appendix A: Table A, C, F in the attached HVAC Sensor Catalog.pdf
Outdoor Temperature Sensor STO100 Order Code 5141100010 Part Number STO100 System Vista, Xenta
Outdoor Temperature Sensor STO200 Order Code 5123246000 Part Number STO200 System I/NET
Outdoor Temperature Sensor STO500 Order Code 5141104010 Part Number STO500 System Continuum
Outdoor Temperature Sensor STO600 Order Code 5126060000 Part Number STO600 System Satchwell
Outdoor Temperature Sensor STO600D Order Code 5126000000 Part Number STO600D System Drayton

Outdoor Temperature Transmitters
STO300
The STO300 transmitter is supplied as a complete unit, comprising a sensing element and an amplifier mounted in a housing which is resistant to ultraviolet light. The transmitter is intended for mounting on an outside wall, on the north side where possible. The transmitter is connected over a 2-wire cable, which serves both as power supply and signal transmission. The reading of the measured signal is made over an external load resistance.
Outdoor Temperature Sensor STO300 -50/50 Order Code 006920501 Part Number STO300 -50/50 System All

Note for each of these outdoor sensors, find the Description, the Order Code, Part Number, and the System it works with for the iBAS (intelligent Building Automation System)

Please note the difference in Weatherproof and Outdoor. I put a lot of these outdoor sensors in at a university in Texas, and always installed in places that were a little protected. I found that under porches, up under the eves and out of the sun, or along a loading dock out of the rain and ice gave me accurate readings.

Swimming Pool: In the piping system of a swimming pool is a corrosive environment with steadily harmful and gradually destructive minerals and chlorine in the water which present a challenge finding sensors able to withstand for extended periods of time.

Schneider Electric makes several immersion temperature sensors. Beginning on page 12 of the above HVAC Catalogue, there is a variety of immersion sensors for the different iBMS lines. 

One example is the STP660 is a Temperature Sensor for the European market, and intended for immersion mounting in pipe or the circulating systems. The stainless steel probe is a good solution but remember,  if the sensor is to be installed in pool water that contains chlorine, the best bet is to use a stainless steel pocket. I suppose it all depends on if sensor is in pipe associated with the secondary pool side of the system or the heating side of the system. If the sensor head is in an area exposed to Chlorine, then there may be an issue. 

Chlorine may attack the solder connections of the wired joints inside the sensor. In the old days products from Satchwell used to produce special sensors for such applications where the wire connections were varnished in order to prevent corrosion. I think at the end of the day, our sensor would have a similar life expectancy to other devices in the plant that were no designed for use in such corrosive atmospheres.

Explosion proof sensors: Schneider Electric does not manufacture explosion proof sensors. We do not partner with another manufacturer who provides such sensors. The closest is an 3rd party explosion proof enclosure with one of our available sensors. Our sensors are designed for building installations and if in extreme environments, we suggest enclosures.


 

Labels (5)
Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
  • Field Devices
  • TAC INET
  • TAC Vista
Attachments
Tags (2)
  • Find more articles tagged with:
  • 5873
  • oat
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore