Sensor characteristics for the Satchwell controller type sensors.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Sensor characteristics for the Satchwell controller type sensors.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Gary
    Gary
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2623 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Sensor characteristics for the Satchwell controller type sensors.

Picard Product_Support
‎2018-09-10 05:05 AM

Issue

Resistance readings

Environment

Sensor

Resistance

Chart

Type

T

Cause

Resistance

Resolution

SENSOR CHARACTERISTICS

  DRT DOT   DD 1401 DW 1202   DW 1204 DWS 1202   DO 2202 -40 to+40'c  
  DDT DWT   DR 2253 DWS 1301              
  DST DOS                    
                         
  Sontay Type SAT 1   Sontay Type SAT 2   Sontay Type SAT 3   Sontay Type SAT 4  
                         
  °C Ohms   °C Ohms   °C Ohms   °C Ohms  
                         
  -40 9711   0 2094   20 2708   -40 2317  
  -35 9604   1 2079   25 2592   -35 2246  
  -30 9465   2 2063   30 2474   -30 2163  
  -25 9288   3 2046   35 2346   -25 2067  
  -20 9067   4 2027   40 2216   -20 1962  
  -15 8796   5 2010   45 2086   -15 1849  
  -10 8472   6 1992   50 1950   -10 1733  
  -5 8093   7 1973   55 1818   -5 1617  
  0 7661   8 1953   56 1792   0 1504  
  5 7182   9 1934   57 1766   5 1397  
  10 6667   10 1911   58 1741   10 1298  
  15 6126   11 1892   59 1718   15 1208  
  20 5573   12 1872   60 1694   20 1128  
  25 5025   13 1851   61 1669   25 1057  
  30 4492   14 1830   62 1646   30 996  
  35 3987   15 1809   63 1622   35 942  
  40 3518   16 1787   64 1600   40 897  
  45 3089   17 1764   65 1578        
  50 2702   18 1740   66 1553        
  55 2358   19 1716   67 1530        
  60 2056   20 1690   68 1508        
  65 1792   21 1667   69 1484        
  70 1563   22 1644   70 1461        
  75 1364   23 1621   71 1439        
  80 1193   24 1596   72 1417        
  85 1047   25 1574   73 1396        
  90 921   26 1549   74 1375        
  95 815   27 1524   75 1353        
  100 722   28 1500   76 1333        
  105 643   29 1476   77 1312        
  110 575   30 1452   78 1293        
  115 517   31 1430   79 1276        
  120 466   32 1406   80 1258        
  125 423   33 1383   81 1240        
  130 386   34 1359   82 1222        
  135 353   35 1336   83 1205        
  140 324   36 1312   84 1188        
  145 300   37 1289   85 1171        
  150 278   38 1267   86 1154        
        39 1243   87 1138        
        40 1219   88 1122        
        41 1198   89 1107        
        42 1176   90 1089        
        43 1155   91 1075        
        44 1134   92 1061        
        45 1113   93 1047        
        46 1092   94 1033        
        47 1072   95 1020        
        48 1052   96 1004        
        49 1033   97 991        
        50 1013   98 978        
              99 964        
              100 950        
                         

Click here to download a pdf with this information.

Labels (3)
Labels:
  • Field Devices
  • Satchwell BAS & Sigma
  • Satchwell MicroNet
Attachments
Tags (1)
  • Find more articles tagged with:
  • 6803
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of