Sending Secure email to SMTP host from Tridium Jaces

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Sending Secure email to SMTP host from Tridium Jaces
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RandyDavis
    RandyDavis

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2185 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Sending Secure email to SMTP host from Tridium Jaces

Guinan RandyDavis Guinan
‎2020-03-04 01:04 PM

on ‎2020-03-04 01:04 PM

Issue

How do I configure outbound email to satisfy a hosting service that requires SSL/TLS

Product Line

TAC IA Series

Environment

  • ENC-410
  • ENC-520
  • JACE-2

Cause

Many SMTP(email) host no longer except non-secure email for transmission.  They require, at minimum, SSLv3 inbound messages.

Resolution

The devices mentioned in the "Environment" section all use the IBM J9 Java Virtual Machine and can not be configured for the minimum secure socket the hosts require.  You must upgrade this hardware if you want to use one of these secure SMTP Host providers. If you are unsure of the JVM on the device, look at the Platform of the device.; The Jace 6E/645 and the Jace 8000 use the Oracle-Sun HotSpot JVM and meet the requirements.

ENC 520 (J404) unsupported SSL/TLS

JVM_ENC.jpg

Jace 6E-645 Supported TLS using the Oracle-Sun Hotspot JVM

JVM_6E.jpg

Jace 8000 Supported TLS using the Oracle-Sun Hotspot JVM

JVM_Jace8000.jpg

Labels (1)
Labels:
  • TAC IA Series
Tags (9)
  • Find more articles tagged with:
  • email
  • ENC 645
  • enc-520
  • Jace 6E
  • Jace 8000
  • RandyDavis20
  • smtp
  • ssl
  • tls
Was this article helpful? Yes No
50% helpful (1/2)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore