Security Expert: Unable to generate list of Users of Active Directory's Sub-Domain

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Security Expert: Unable to generate list of Users of Active Directory's Sub-Domain
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1133 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Security Expert: Unable to generate list of Users of Active Directory's Sub-Domain

Lieutenant JG JamesMorgan Lieutenant JG
‎2022-12-13 08:49 AM

Last Updated: Crewman ContentModerator ‎2025-09-01 03:33 AM

Issue

Note: To enable Windows Authentication login in Security Expert, the following are required:

 

  • SX-AD-USR: Active Directory User Integration License.
  • During Security Expert installation, "Enable Windows Authentication on Data Service / Client Communications" must be enabled.
  • In Security Expert Client: enable "Use Windows Authentication" Found in Global | Operators| Configuration section.

    Sx client Win Auth.png

A site has the domain abc.xyz.com (Where ABC is the domain and XYZ is the sub-domain)
When Windows Authentication is enabled, users on the sub-domain (i.e: XYZ\username) are not visible in AD Search (found in  Security ExpertX Client: Global | Operators| Username field| ellipsis [...]). Because of this, It is not possible to directly connect operators with AD sub-domain users.

Product Line

EcoStruxure Security Expert

Environment

Security Expert Server

Warning

Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support for assistance.

Cause

This is an Active Directory design. The Search feature for Active Directory users will have the same visibility as the machine it's installed on. (In this case, the machine was joined to the ABC domain and this is the domain Security Expert is able to pull information from). XYZ Sub-domain users might have permission to access the ABC domain but they are not on the domain. Therefore, Security Expert can't search for them.

Resolution

Security Expert, the machines and the users must be on the same domain:

Solution 1:

Manually adjust the domain on the login page ex: "XYZ\username"

  • The XYZ sub-domain users must have ABC privileges.

 

Solution 2:

Create duplicate users on the ABC domain

  • This is a temporary solution because you will be left with duplicate users

 

Solution 3: 

Change the domain structure in Active Directory to match the users, workstations and Security Expert client/server on the same domain

 

Labels (1)
Labels:
  • EcoStruxure Security Expert
Tags (1)
  • Find more articles tagged with:
  • JamesMorgan22
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore