Secure AIC: Control of Entry and Exit to Zones

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Secure AIC: Control of Entry and Exit to Zones
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • SESA128071
    SESA128071
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1288 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Secure AIC: Control of Entry and Exit to Zones

Picard Product_Support
‎2018-09-07 12:14 AM

Last Updated: Administrator DavidFisher Administrator ‎2020-10-23 09:28 AM

Issue

  1. There needs to be a way to restrict the number of people gaining access to the door.
  2. There needs to be a way to keep up with how many people are in the Zone.

Product Line

TAC INET

Environment

Access Initiated Control

Cause

I/NET Seven allows configuring a door to have both an entry and an exit reader and uses the selection of Anti-passback/Anti-tailgate to set up Zones or areas with stricter control over access. However, even with the Anti-passback option set to Hard which denies access to successive reads at the same reader, it does not prevent multiple persons from entering and exiting together and it does not provide real time accounting for the number of people in a Zone. Other than having a guard at the door the usual method of implementing Zones does not prevent violations. The example below presents some thoughts about how to improve the security of the Zone in an INET Seven system.

Resolution

One method to accomplish the first goal is to use a two door egress system as is often used in jails and similar security setups.  For a medium security setup where the intent is not to prevent people from leaving only one of the doors needs to have a card reader.  Such a design is illustrated below:

securezone.png

 

Notes:

  1. Electric strike normally energized.
  2. Low walls or fences. The area should be small enough to limit how many people or things are in it at one time.
  3. Gate with normally de-energized bolt.  The gate could swing both ways so one would only have to push it to open it. It should have a spring to close it.

The door "a" would have both an Entry and Exit reader so Anti-pass back/Anti-tailgate can be implemented. The strike on door "a" would be normally energized and be opened by a valid reader transaction.

The bolt on the gate would be normally de-energized allowing the gate to open freely.  When the strike on door "a" is de-energized, the bolt on the gate would be energized preventing the gate from opening. This is designed to allow only one person to move into or out of the Zone at one time.

An added level of security would be accomplished by mounting IR emitter/receiver pairs along the low wall or fence at regular intervals.  A person would interrupt the light at a limited number of receivers so if more than expected are interrupted it would be a violation of one person at a time and necessary action could be taken.

If material needed to be moved through the door the gated area could be made large enough to allow for a dolly or whatever might be needed.  A different access level would be provided to those who are moving material thus preventing the alarm for too many people going through the door.

This approach would restrict movement into and out of the Zone and the example given in the AIC note could be implemented to allow real time monitoring of occupancy levels in the Zone.

Design thoughts:

To calculate whether more than one person is in the gated area, sum the number of receivers that are detecting and compare it to a minimum, e.g. four of six must be detecting if only one person is in the area.

If material is in the gated area generate an alarm if an authorized card is not read.  Use the alarm delay for the point to give an individual time to make a card read before sounding the alarm.

The AIC scheme described in the AIC note would have to be duplicated for the material mover individuals to change the calculation of a person in the gated area.  For material movers the detection would be (sum of detectors < minimum) whereas for regular individuals the detection would be (sum of detectors > minimum).  Remember the SLI connected to this door can have only 64 AIC’s and this door now has used 2 of them

Use an inter-card delay long enough to let the person to get out of the gated area before another card can be read.

For personnel safety there must be a way to de-energize the strike.  One method would be to mount an emergency exit button located far enough away from the door so a single person would not be able to reach it and a second emergency exit button on the outside of the Zone so someone could keep the strike de-energized until everyone is evacuated.  Most codes probably require that all strikes be de-energized in case of smoke or similar emergency so that would provide another fail-safe.

Labels (1)
Labels:
  • TAC INET
Tags (1)
  • Find more articles tagged with:
  • 2004
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore