Script advise for xPDisplay on a b3 controller in StruxureWare Building Operation

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Script advise for xPDisplay on a b3 controller in StruxureWare Building Operation
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Dave_Shore
    Dave_Shore
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3160 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Script advise for xPDisplay on a b3 controller in StruxureWare Building Operation

Picard Product_Support
‎2018-09-06 12:07 PM

Last Updated: Dave_Shore Schneider Alumni (Retired) ‎2024-01-25 12:52 AM

Issue

Script advise for xPDisplay on a b3/i2 controller

Product Line

EcoStruxure Building Operation

Environment

  • i2 and b3 Controller
  • xP Display

Cause

The xP Display was designed when only Continuum was available (before EBO) and there was no documentation for EBO. Scripts need to be used to control the xP Display

Binding to Object LCDAnswerString directly via "String Input" or "String Output" in a script program

Then doing a check 
If LCDAnswerString <> ""  then
causes the script to disable with errors.

"" = Null

Resolution

A simple way around this is to do the script check on another (manually created) string that is bound to the object LCDAnswerString
Thus the following will work:

 Numeric Input LCDKeyStroke       'bind to LCDKeyStroke    - this can also be used to set to zero. eg. LCDKeyStroke = 0
String Input LCDAnswerStrCopy   'bind eg LCDAnswerStrCopy  - use this to read the LCDAnswerString value
String Output LCDAnswerString    'LCDAnswerString  - use this to set to Null eg. LCDAnswerString = ""
Numeric Output AAA

Line Wait4Value
If LCDAnswerStrCopy <> "" then  'check if a value has been input
   AAA = minimum(maximum(0, StrToNum(LCDAnswerStrCopy)), 100) 'Make AAA equal the input (min0, max100)
   LCDAnswerString = ""     'reset LCDAnswerString back to Null
Endif

Outside this script, the manually created string object LCDAnswerStrCopy needs to be bound to LCDAnswerString, this can be achieved directly (change the binding type to COV) or via another script (use Print LCDAnswerString to LCDAnswerStringCopy)

Note

v4.0 export, script text attached and install guide attached

Labels (1)
Labels:
  • EcoStruxure Building Operation
Attachments
Tags (5)
  • Find more articles tagged with:
  • 8356
  • acclcdanswerstri
  • acclcdkeystroke
  • DavidShore19
  • DavidShore24
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore