Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Script Program Error “Datetime calculation with overflow”

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Script Program Error “Datetime calculation with overflow”
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • GavinHe
    GavinHe
Related Products
product field
Schneider Electric
EcoStruxure™ Building Operation

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
2 Likes
2335 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Script Program Error “Datetime calculation with overflow”

Sisko GavinHe Sisko
‎2022-08-22 01:52 AM

on ‎2022-08-22 01:52 AM

Issue

Script program Halts with error “Datetime calculation with overflow” resulting in the program not controlling

Product Line

EcoStruxure Building Operation

Environment

Observed in versions 4.0.1.86 and 4.0.3.176

Cause

When a script program subtracts one datetime from another it can result in a negative value if the datetime being subtracted (subtrahend) is a later datetime than the one being subtracted from (minuend).  This causes the program to halt with error “Datetime calculation with overflow”.  The issue can also occur when a script program calls a function that involves a datetime subtraction resulting in a negative value, for example the standard PID function.

 

The image below illustrates the issue where DT1 is a later time than DT2.

 

ScriptErrorRedBoxes.png

 

The problem has typically been seen to occur when using the PID function and the ASP is set to obtain updates from an NTP server.  The PID function uses the current time and the last time the function was called to calculate the time passed, for example: -

 

TimePassed = CurrentDate – LastTime

 

Ignoring the date portion consider the scenario where the ASP time is currently 14:01:00 but is one minute ahead of the actual time of the NTP server.  If the function has just been called the LastTime variable will be 14:01:00.  However, in the meantime if the ASP time is updated by the NTP server it becomes 14:00:00 and hence when the function is called again the calculation is: -

 

TimePassed = 14:00:00 – 14:01:00 

 

This results in a negative value halting the program on error “Datetime calculation with overflow”.

 

Resolution

Either of the two workarounds below can be used but each will need to be considered based on their overall impact. 

 

  1. Use the DIFFTIME function
  2. If calling a function check the subtrahend is not a later datetime than the minuend before calling.

 

This is reported in defect #50263

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (1)
  • Find more articles tagged with:
  • GavinHeward22
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore