Issue
The FDA requires Building Automation systems to meet their standards which are outlined in Chapter 21 CFR and FDA Part 11.
Environment
- Vista
- I/NET
- Andover Continuum
- TAC I/A-series
- Satchwell Sigma
Cause
Finding documentation on Schneider Electric Building Automation Systems which comply to The Food and Drug Administration rules.
Resolution
- I/NET - currently unavailable
-
Andover Continuum
With the addition of the 21 CFR Part 11 compliance pack, Continuum can meets these requirements.
-
Satchwell Sigma
SoftwareOverview.pdf
Advanced Security Module.pdf
Note: Validation to 21CFR Part 11 can only be performed on whole operational systems and as such, a sub-system comprising the Satchwell Sigma building management system cannot be validated in it own right. Satchwell Sigma would normally be validated as part of a whole operational system.
- TAC I/A Series - currently unavailable