Sample PE program to control access by forklift operator to storage cage gate

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Sample PE program to control access by forklift operator to storage cage gate
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RandyDavis
    RandyDavis
  • AbeMeran
    AbeMeran

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1023 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Sample PE program to control access by forklift operator to storage cage gate

Captain AbeMeran Captain
‎2022-08-10 08:13 AM

on ‎2022-08-10 08:13 AM

Issue

Need sample PE program for control of access to a storage cage gate by forklift operators where the gate is required to stay open (up) until the forklift operator cards at the reader a second time on his/her way out of the cage.

Product Line

Andover Continuum

Environment

  • Continuum Net Controller II
  • Continuum ACX 2 Controller
  • Continuum ACX 4 Controller

Cause

Continuum PE programming guidelines

Resolution

This sample program was provided as proof of concept only and not intended as a complete solution to the use case.

SampleCageGateProgram.PNG

 

Object : StorageCageControl
 Type : InfinityProgram
 LastChange : 1/29/2020 11:29:14 AM
 DeviceId : PSS\ACX2.10
 Alias : StorageCageContr
 CreateTime : 1/29/2020 9:59:56 AM
 CreatedBy : Root\Acc
 TimeLocked : 1/29/2020 11:29:14 AM
 InstanceId : 7003/7002
 ByteCode : 
'SAMPLE program for controlling access to a Storage Cage gate 1/29/2020 AM

'Program is LOOPING/AUTOSTART

'

'DESCRIPTION

'On valid access to the cage by forklift operator, program will unlock the gate using the

' PermanentUnlock property to keep it unlocked until the forklift operator indicates the gate

'can be closed by presenting his/her card at the card reader.

'

'REQUIREMENTS

'1. ACX2 or NC2 controller only, program wont work in NC1 or old ACX7xx as they don't support the PermanentUnlock flag

'2. Set the StrikeTime attribute of the door controlling the gate to ZERO

'3. Create GateLeftOpenALM InfinityNumeric, and attach to an alarm (Optional)



Numeric CloseTimeOut



Line Init

  CloseTimeOut = 15 'Notify gate may have been left open after CloseTimeOut minutes.

  Goto WaitToOpen



Line WaitToOpen

  GateLeftOpenALM = False

  If CageGate ValidAccess then

    CageGate PermanentUnlock = True

    Goto WaitToClose

  Endif



Line WaitToClose

  If CageGate ValidAccess then

    CageGate PermanentUnlock = False

    Goto WaitToOpen

  Endif



  If TM >= CloseTimeOut then GateLeftOpenALM = True 'Gate may have been accidentally  left open 



Line E

'oops, runtime error, wait a bit then try again

  If TS > 30 then Goto Init

 EndByteCode
 Status : Active
EndObject
Labels (1)
Labels:
  • Andover Continuum
Tags (5)
  • Find more articles tagged with:
  • AbeMeran22
  • access
  • control
  • pe
  • program
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore