Safe Connection Practices for Flex Server

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Safe Connection Practices for Flex Server
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Mukesh_Sangwan
    Mukesh_Sangwan

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
452 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Safe Connection Practices for Flex Server

Ensign Mukesh_Sangwan Ensign
‎2025-09-17 05:22 PM

on ‎2025-09-17 05:22 PM

Issue

The Flex Server fails to power ON or boot up after first installation

Product Line

EcoStruxure Building Activate

Environment

  • ESXBFXSVR00B008
  • ESXBFXSVR0BC008
  • ESXBFXSVRBCW008

Warning

Hazard of Electric Shock: Remove all power from all devices before removing any covers or doors of the system. Disconnect power at the device and at the power source.

Electrostatic Discharge Required: Always discharge static electricity from your person by touching metal prior to handling any hardware. Failure to do so may result in damage to devices.

Cause

“Live Insertion” of power supply to the Flex Server or “Hot plugging” the RS485 connector to the Flex Server can lead to internal component failures. These acts can induce transient voltage that exceed the design tolerances of sensitive components. These transients may cause internal components to fail, leading to MODBUS failures or Gateway boot-up failures.

 

What is “Live insertion”?

“Live insertion” is the act of connecting or disconnecting a power connector to the device while the power supply is energized (powered ON).

Mukesh_Sangwan_0-1758126716078.png

 

What is “Hot Plugging”?

“Hot plugging” refers to the practice of connecting or disconnecting a device to a system while it is powered on and running, without shutting down the system.

Mukesh_Sangwan_1-1758126783547.png

 

Resolution

To protect the Flex Server and ensure long-term reliability, always adhere to the following steps (Safe Connection Procedure) when connecting or disconnecting the DC power supply or RS485 connectors:

  1. Connection Procedure:
    1. Before connecting or disconnecting the power supply or RS485 connectors, ensure the mains power supply for both the RS485 devices and FlexServer power adapter is completely switched off.
    2. Connect the DC terminal block and the RS485 terminal block to the correct sockets firmly, ensuring proper alignment and contact to avoid intermittent connections.
    3. Power on the power supply only after all connections are completed.
       
      Mukesh_Sangwan_3-1758127126091.png

       

  2. Disconnection Procedure:
    1. Before removing the DC terminal block and RS485 terminal block connectors, switch off the power supply first, verify it is de-energized.
    2. Then carefully disconnect the DC power supply and RS485 connectors.Mukesh_Sangwan_4-1758127221896.png

       

Labels (1)
Labels:
  • EcoStruxure Building Activate
Tags (1)
  • Find more articles tagged with:
  • MukeshSangwan25
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore