Issue
STR-350 will not send a service pin message.
Environment
STR-350
LNS Database
Cause
If the STR-350 has been commissioned previously then deleted from the LonMaker database it will not send out a service pin message until taking the steps below.
Resolution
Manually enter the Neuron ID of the STR-350 and commission it into the network. This will restore the service pin functionality.