STD300: Will it require calibration when connected to a Xenta controller?
  • STD300: Will it require calibration when connected to a Xenta controller?
  • SESA150559
    SESA150559
‎2018-09-06 10:57 AM
Calibration requirement?
STD300:
006920121 STD300-300 -50/50
006920141 STD300-300 0/100
Some sensors on the market requires calibration when connected to the controller, in order to function properly.
No calibration is required when connecting the STD300 to a Xenta controller. The sensor is using a 4-20mA output signal, so the controller needs to be configured for this type of signal in order to work with this sensor.
Labels (2)
  • Field Devices
  • 11547