SQL Equalization Failure on Non-English Systems

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • SQL Equalization Failure on Non-English Systems
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Derrick_Ratliff
    Derrick_Ratliff
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1223 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

SQL Equalization Failure on Non-English Systems

Picard Product_Support
‎2018-09-06 01:46 PM

Issue

SQL Equalization Failure on Non-English Systems

Environment

I/NET

File Equalization

Client Computer

Cause

There is a collation mismatch that was caused during the SQL installation.

Resolution

  1. Go to the Client PC
  2. Demote the client PC to Standalone
  3. Create a Temporary Folder on the C Drive, for example C:\Equalization
  4. Run the SQL Express install file
  5. Wait for the installation shell to start, but do not hit NEXT
  6. Browse to your C: Drive and look for a temporary folder with a current time stamp. This will likely have a name made of random numbers and letters
  7. Open this folder and copy the contents to your temporary folder. You may need to copy each file manual as a file beginning in $ will not copy.  You do not need this file.
  8. Cancel out of the SQL Express installation program
  9. Open the Command Prompt
  10. Browse to the temporary folder you copied files to
  11. Type in the following exactly, but replace *** with the sa password for your system
    This doesn't make any sense to me, any time the text on a link passes the end of the line the line is supposed to wrap to the next line

    setup.exe /QUIET /ACTION=REBUILDDATABASE /INSTANCENAME=MSSQLSERVER /SAPWD=***
    /SQLSYSADMINACCOUNTS=Administrator /SQLCOLLATION=SQL_Latin1_General_CP1_CI_AS
     
  12. This will run a limited version of the SQL installation.  Follow the instructions as prompted
  13. Re-promote the PC to Equalized client.
  14. Manually delete the temporary folder you created in step 3
Labels (1)
Labels:
  • TAC INET
Tags (1)
  • Find more articles tagged with:
  • 5291
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore