SPD910 hysteresis
  • SPD910 hysteresis
  • SESA150559
    SESA150559
SPD910 hysteresis
‎2018-09-06 10:56 AM
Details on hysteresis of the SPD910 series sensors
004701090 SPD910
2000Pa Switch Pres Air
004701080 SPD910
1000Pa Switch Pres Air
004701070 SPD910
500Pa Switch Pres Air
004701060 SPD910
300Pa Switch Pres Air
In some applications the hysteresis of the sensor is important
There are 2 types which can switch the 300 Pa:  - SPD910-300Pa and SPD910-500Pa.
The hysteresis or switching differs from type to type because of range and the clip feather.
In general they are as follows:
SPD910-300Pa             0,1mbar +/-15%
SPD910-500Pa             0,2mbar +/-15%
SPD910-1000Pa           0,4mbar +/-15%
SPD910-2000Pa           1,0mbar +/-15%