SPD310 / SPD360 symmetrical configuration
  • SPD310 / SPD360 symmetrical configuration
  • SESA150559
    SESA150559
‎2018-09-06 10:40 AM
If using the "sym" jumper in a 100Pa configuration, will this mean -50Pa - +50Pa range?
004700320 SPD310-100/300/500/1000 Pa
004700340 SPD310-1000/1200/2500/5000 Pa
004700360 SPD360-300/500/1000/2500 Pa
In some applications, the output signal, is requested to be symmetrical.
The specified values we can grant is only down to 100 Pa.
Using the Sym – jumper configuration would change the signal to -100 Pa …+100 Pa ( not -50…+50 Pa ), because the sensitivity of the sensor does not change by this jumper.