SNVTs supported in Xenta server 5.1.6

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • SNVTs supported in Xenta server 5.1.6
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Product_Support
    Product_Support
  • sesa177673
    sesa177673

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
941 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

SNVTs supported in Xenta server 5.1.6

Picard Product_Support
‎2018-09-06 01:09 PM

Issue

Are the following SNVTs supported in Vista 5.1.6?

  • SNVT_Amp_ac
  • SNVT_Count_32
  • SNVT_Volt_ac

Environment

Xenta X5XX, X7XX, X9XX with firmware 5.1.6

Cause

The SNVTs  SNVT_Amp_ac, SNVT_Count_32 and SNVT_Volt_ac are not included in the Xenta 5.1.6 firmware. They will be included in 5.1.7. There is however a workaround available in 5.1.6 

Resolution

  1. Locate the SNVTtype.def file in the Xenta server.
    Connect to the Xenta server using an FTP client and locate the SNVTtype.def file under configdb/Lon/SNVTTYPE.def.
  2. Copy the file to your PC and make a backup copy
  3. Edit the file with a suitable text editor (notepad, notepad2 etc)
    -Locate the SNVT_amp definition
    -Add the following lines after SNVT_amp definition (see screenshot below):
    //---//
    amp_ac
    139
    2
    1  
    INTEGER,,2,0,65535,1,0
    //---//

  4. Repeat the process with the other 2 SNVTs
    - SNVT_count_32:
    Add the following lines after SNVT_count definition:
    //---//
    count_32
    183
    4
    1
    INTEGER,,7,-2147483648,2147483647,1,0,raw
    //---//


    - SNVT_volt_ac:
    Add the following lines after SNVT_volt definition:
    //---//
    volt_ac
    138
    2
    1  
    INTEGER,,2,0,65535,1,0

    //---//
  5. Replace the SNVTType.def file in the Xenta server using the FTP client.
Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 6552
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore