Issue
Adding a device through the System Plug-in results in missing SNVTs, SCPTs, or Module/Functional Block Names in the Vista database.
Environment
Vista 5.x.x
Cause
The XIF file is either incorrect or parsed improperly.
Resolution
- Right click on the device and select properties.
- Click on the XIF file tab.
-
View the XIF file name (this can be found in the $thisfil directory of the Vista database) and either browse in a renamed copy of the existing file or an independent copy of the file by clicking the ... button.
- Click Ok
- Log out of Workstation
- Log into Workstation to see the changes.
Note: For a change to be detected the filename or location of the file must be different.